what is impedance of transformer?
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
The percentage impedance of a transformer is the volt drop
on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
| Is This Answer Correct ? | 63 Yes | 8 No |
Answer / rated kuldeep
Well friends--- % impedance is defined as the ratio of
impedance voltage(the voltage at rated frquency applied to
one winding and other winding kept short circuit to flow
full rated current in circuit) to the rated voltage of the
transformer... Correct if i m wron g.
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / montu
Percentage Impedance (Z%)
The impedance of a transformer is marked on most
nameplates - but what is it and what does the Z% figure
mean?
Definition
The percentage impedance of a transformer is the volt drop
on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
It is also the percentage of the normal terminal voltage
required to circulate full-load current under short circuit
conditions
Measuring Impedance
The impedance is measured by means of a short circuit
test. With one winding shorted, a voltage at the rated
frequency is applied to the other winding sufficient to
circulate full load current - see below:
The percentage impedance can then be calculated as follows:
Z% = Impedance Voltage x 100
Rated Voltage
Changing the Impedance Value
The most economical arrangement of core and windings leads
to a 'natural' value of impedance determined by the leakage
flux. The leakage flux is a function of winding ampere
turns and the area and length of the leakage flux path.
These can be varied at the design stage by changing the
volts per turn and the geometric relationship of the
windings.
The Effect of Higher and Lower Impedances
The impedance of a transformer has a major effect on system
fault levels. It determines the maximum value of current
that will flow under fault conditions.
It is easy to calculate the maximum current that a
transformer can deliver under symmetrical fault
conditions. By way of example, consider a 2 MVA
transformer with an impedance of 5%. The maximum fault
level available on the secondary side is:
2 MVA x 100/5 = 40 MVA
and from this figure the equivalent primary and secondary
fault currents can be calculated.
A transformer with a lower impedance will lead to a higher
fault level (and vice versa)
The figure calculated above is a maximum. In practice, the
actual fault level will be reduced by the source impedance,
the impedance of cables and overhead lines between the
transformer and the fault, and the fault impedance itself.
As well as fault level considerations, the impedance value
also:
determines the volt drop that occurs under load - known
as 'regulation'
affects load sharing when two or more transformers operate
in parallel
Sequence Impedance (Z1 Z2 Z0)
The calculation above deals with a balanced 3-phase fault.
Non-symmetrical faults (phase-earth, phase-phase etc) lead
to more complex calculations requiring the application
symmetrical component theory. This in turn involves the
use of positive, negative and zero sequence impedances
(Z1, Z2 and Z0 respectively).
As with all passive plant, the positive and negative
sequence impedances (Z1 and Z2) of a transformer are
identical.
However, the zero sequence impedance is dependent upon the
path available for the flow of zero sequence current and
the balancing ampere turns available within the
transformer. Generally, zero sequence current requires a
delta winding, or a star connection with the star point
earthed. Any impedance in the connection between the star
point and earth increases the overall zero sequence
impedance. This has the effect of reducing the zero
sequence current and is a feature that is frequently put to
practical use in a distribution network to control the
magnitude of current that will flow under earth fault
conditions.
regards
dhruv shah
G.T.P.L
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / mahesh-lanco
The percentage impedance of a transformer is the volt drop
on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
The Impedance(between primary Secondary) of the Ideal
Transformer is Infinity.As there is no current conduction
path b/w primary and secondary as the energy conversion is
beacuse of induction only.I.e.,Current Between Primary and
secondary is Zero and Impaedance is Infinity..
It is th question iam faced in My interview.
Hope this may useful for you.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / j.vinothkarthick
hi kuldeep you saying ratio between impedence voltage to
rated voltage...... is this really correct ah ??????
impedence is the ratio of voltage to current is it?????can
you explain me abt this?????????
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / aizaz khan
Impedance of transformer (Z), is the total opposition that
a circuit presents to alternating current
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / akash
impedance is total resistance offered by the circuit & in
transformer there is a leakage flux due to windings in air
expressed as leakage reactance and resistance drop in
windings so the vector addition gives impedance.
| Is This Answer Correct ? | 8 Yes | 18 No |
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
when transformer oil should be filtered/tested?
How capacitor improves pf
what is zinc diffusion?
why we step up voltage for reducing the loss, even if voltage and current are proportional anr resistance remains same
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
why mccb is not tripping when phase & neutral terminal are interched ?
in gen traf what is ONAN , ONAF , OFAF and DYN
For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of 4-pole ACB or any switchgerar..Please guide me why is it so????
4 Answers Piramal Glass Limited,
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
differnce between single acting and double acting solenoid valves
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)