For Synchronisation of DG Sets Sometimes we people use NIC
(Neutral Isolation Contactor) Instead of 4-pole ACB or any
switchgerar..Please guide me why is it so????
Answers were Sorted based on User's Feedback
Answer / srikanth shreenidhi
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / vinod
when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / muniraja1283@rediffmail.com
above said subject full very satisfactury
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / zuber ahamed
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
Is This Answer Correct ? | 1 Yes | 5 No |
what is encoder & its use?
what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)
what is the function of garing capacitir in SF6 circuit braker?
My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?
why we create vaccume in transformer tank before oil filteration?
In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?
how starting current in motor is reduced in case of motor in star connection.
how will calculate the safe starting current of 3-phase squirrel cage induction motor?
DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?
Please give me a solid reason there are 2 ELCB's If we take Phase from ELCB NO:1 an Netural from ELCB N:2 why ELCB is tripping when we connect the Load?please brief me with detail
why transmiision rating in kva?
in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?