Answer / srikanth shreenidhi

Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker

However when only one DG set is used we always go with 4
pole breaker.

Is This Answer Correct ?    16 Yes 8 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / vinod

when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.

Is This Answer Correct ?    9 Yes 1 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / muniraja1283@rediffmail.com

above said subject full very satisfactury

Is This Answer Correct ?    3 Yes 4 No

For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of..

Answer / zuber ahamed

Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker

However when only one DG set is used we always go with 4
pole breaker.

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

what is encoder & its use?

1 Answers   ACC,


what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)

0 Answers  


what is the function of garing capacitir in SF6 circuit braker?

1 Answers  


My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?

6 Answers  


why we create vaccume in transformer tank before oil filteration?

3 Answers   CG CoreEL,






In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?

2 Answers   GE,


how starting current in motor is reduced in case of motor in star connection.

4 Answers   Adhunik,


how will calculate the safe starting current of 3-phase squirrel cage induction motor?

0 Answers  


DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?

1 Answers  


Please give me a solid reason there are 2 ELCB's If we take Phase from ELCB NO:1 an Netural from ELCB N:2 why ELCB is tripping when we connect the Load?please brief me with detail

3 Answers  


why transmiision rating in kva?

4 Answers  


in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)