Answer / v.senthilkumar
To measure insulation resistance of 11KV cable between core
& armour, we can use 5kv megger for 60 Sec.
Is This Answer Correct ? | 22 Yes | 2 No |
Answer / thowsif_emerson_csm team
To measure insulation resistance of 11KV cable between core
& armour,
Test voltage is 28KV(RMS Value)
Duration is 300 Sec...
Is This Answer Correct ? | 10 Yes | 6 No |
11 kv cable resistance we can measure
Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sujeet pandey
To measure the insulation resistance of 11kv cable, we need
to keep Megger test voltage at 1kv and take 2 readings; one
at a interval of 15 sec and other at an interval of 1 min.
This will give Absorption Factor which is equal to ratio of
resistance at 1 min to the resistance at 15 sec. If the A.F.
is less than 1.2(a/c to Indian Standards) then the
insulation is not good and we must take the remedy action.
Is This Answer Correct ? | 0 Yes | 1 No |
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
What is the ratio of true power to apparent power in an ac circuit?
Why used in layer by layer charcoal and salt used in earth pits.
11 Answers CESC, HP,
Pls tell me what is the exact current conducting capacity of copper and aluminium cables?how much capacity of cables need to 90kw induction motor&how?
For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of 4-pole ACB or any switchgerar..Please guide me why is it so????
4 Answers Piramal Glass Limited,
Single line digram for 11 kV to distribution use go,la and do
why dhyedration test required for transformer oil once in a year
how will u exactly calculate the unit consumption of the Air conditioners?Split/Window/
how we can measure the dc current instead of clamp meter ?
What is use of reactor..how it is help ful in electrical system .....brief explain
What is the direction of rotation of blades in a table fan and in a ceiling fan ?
Which of the following are the important limitations of rod gap surge arresters? 1. They are not capable of selling off power frequency follow up current. 2. After a discharge, the rods are destroyed completely. 3. Performance is affected by climatic conditions. Use the following codes for selecting the correct answer. Codes: (a)1, 2 and 3 (b)1 and 2 (c)2 and 3 (d)1 and 3