To measure insulation resistance of 11KV cable between core
& armour, what should be the test voltage & duration?
Answer Posted / narendra sharma
11 kv cable resistance we can measure
Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....
Is This Answer Correct ? | 4 Yes | 1 No |
Post New Answer View All Answers
how do we calculate length of starting time and repeated starting of a direct online starter?
Why to keep capacitor bank off while generator running.
Between educational qualification and practical work experience, give us a brief explanation on your practical experience in your past Endeavour that you performed well to the satisfaction of your past or present employer?
Pl. share your experience about industrial-electronics repair of machine tool.
What is difference between YNyn0 and YNyn ??
how can maintaince the acb contactor moveing and fixing kit
Why does inductive loads consume KVARs?
WTA used cb?
How to checked frequency drive output voltages?
How many types of circuit loads are there in a common electrical circuit?
What is the disadventage of gland earthing(power cable) if any. ?
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
how are reversing the direction of rotation of dc motor
star delta starter contorl circuit... drawing..
Define pole pitch?