We operate a 10 Mw facility and we have been experiencing
several trips due to fluctuations on the MVAR? We have
checked all issues related to the AVR and we have found all
OK? Can anyone help us? The grid voltage, internal voltage,
all regular parameters look ok. MVAR fluctuate and there it
goes the unit? What could be happening? Thanks!
Answers were Sorted based on User's Feedback
Answer / chaitanya
this may happen due to the variation of reactance produced
by the capacitors connected to that line/....isolate one by
one under observation...and this can be sorted out on
timely basis,,,,
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
I agree with chaitanya this may happen due to the variation
of reactance produced
by the capacitors connected to that line it will be better
to maintain the Power Factor 0.90 only every where and the
next and only cause is that AVR problem may be some loose
connection in power as well as control side because AVR has
to take care of that MVAR.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naresh
this could be because of the interturn winding losses that
takes place in the lines.this factor may increase the MVAR
rating of the system,which infuence the performance of thea
system.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish
Generator AVR have got two setting either to fix MVAR or
according to load if u set them to fix MWAR generation
probably it will solve ur problem to a extent also look at
load pattern first.its really helpfull when you have synch
operation with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.j.pailwan
Please check CT connections, CT Specifications and
saturation of particularly B phase as this CT feed back is
used in AVR during PF control mode while pareller with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
why is the transmission voltage is multiple of 11?
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
What happen to the transformer if the OLTC frequently used for lower and raise occured 50times daily?
what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?
While miss missed name platform fo electric motor how to calculate simple fourmul,?
which safety we have to take when we go for work?
What is thermal relay and how it is works in transformer please explain
Difference between on line capacitor and Station type capacitor
how to calculate circuit breaker capacity
1.how to calculate energy units in our home at singe phase, 2.415V,63A wiring what will use thickness of wire
what is mean by power factor
how to calculate the current carrying capacity of a conductor. How it is related to diameter of cable or conductor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)