after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
| Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the application of Dyn1 and Dyn11 vector group of transformer?
State the points to be considered for selecting a particular type wiring.
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)
What are the types of instrument transformer?
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
What are disadvantages of capacitor
which protection used in power plant?
How to protect sensitive loads such as Dosing pumps inside a factory from voltage surge/voltage fluctuation.
WHAT IS THE difference betwwen LT CABLE AND CONTROL CABLE
Explain RYB?
Why a transformer is known as a static device?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)