after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
Is This Answer Correct ? | 1 Yes | 1 No |
What will happen if the voltage in my house drops from 220V to any lower voltage?
what is the difference between megger and earth resister ??
what is meant by auto transformer?
how to calculate the chiller load from TR to KW?
Define resonant peak?
What are effect of radio system in DCS Distributed control system ?
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
why odd hormonics only will effect the power system.why not even hormonics
send me any model test paper of clerical post of state bank of india.......
What are the voltage values for LT,HT,EHT and other voltages??
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
How to size the Neutral grounding resistor?