Answer / jayesh pillai
star point connected to ground is known as neutral earthing
it is essential for preventing arcing ground effect during
faulty conditions and maintaining zero potential at neutral
even during unbalanced condition
equipment earthing is related to earthing of non current
carrying metallic parts that may be electrocuted during
earth fault. so it is doned in order to prevent any shock
to any person and even equipment when current flows through
such equipment body during fault
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / ramesh kumar
Neutral earthing is return path for current by making earth
as conductor.ie like all Star connedted system are having
return as earth and 3 phases metal conductor.
body earthing is least path for fault curretnt or leagage
current flow by connecting metal body to earth point by cu
conductor.
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / dhananjay kumar ....gpl..
The star point of an electrical machine is earth to
make the neutral point and ground potential is called neutral earthing.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prabhat
neutral earthing is the process of connecting the star point of a 3 phase system to earth whereas equipment earthing is the process of connecting non current carrying part usually the metal frame of an equipment to earth.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dhananjay kumar from japla (gp
The star point of an electrical machine is earth to make the neutral point and ground
potential is called neutral earthing.
This is done so that a number of measurement and protective system
can be suitably connected with the power system.
The equipment earthing is done to protect operating personal to protect them for electrical shok.
In some cases equipment earthing also protect the environment from earthing. .......
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / m. p.renu.
There is an advantage of body earthing and neutral earthing
interconnected, since any single phase connected load if
interchanged, the fuse or the circuit trips indicating the
phase wire is wrongly connected.In any case the earthing
system works when there is a normalleakage and as we have
interconnected the two earthing system the total earth
resistance becomes low & this is an added advantage.
If not so kindly explain.
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / venkat
earhings are 2 types .they are 1)neutral earthing 2)
equipment earthing . neutal earthing is connecting non
metallic part to ground. system earthing is connecting
some part of the system to ground.
Is This Answer Correct ? | 5 Yes | 13 No |
why bucholtz relay placed inclined in transformer?
what is meant by motor protection relay & its working principle ?k
Why carbon brush used in dc motor also why its not used in ac motor?
If breaker is undefined position, first step to do.
How is magnetic leakage reduced?
1 KW = how many HP
What do you mean by a phase angel of instrument transformer?
STATE USE OF ARC RUNNERS & SPLITTERS ?
What will happen when we connect 2 bulbs in series between 2 phases
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
Differentiate between real and apparent power?
what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)