How to check the SCAN time of DCS ,n dont give therotical
answers .How to check the SCAN time of DCS during FAT?
Answers were Sorted based on User's Feedback
Answer / rajkumar
If you are using a DCS (Distributed Control System), there
should be a diagnostic utility that you can run (this is
usually part of the system software). If your sotware scan
is structured correctly i.e. all software is called in
cyclic scans and not free scans, the utility should be able
to tell you the loading of these scan cycles.
You should also be aware that you are doing this under FAT
conditions. This would imply that most of your IO are not
connected, which in turn would push up your scan times for
all the diagnostic alarms comming in.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rnm
In my opnoin, Sacn time checking during FAT shall be input
simulation with one repeater block. Then go for cycle sacn
rate check, which will cover input,process block(PID) and
output. We know, there wiil be no O/P connected in field
and no much execution of loops. In this case, very
difficult to conclude this time.Better to check I/O
scanning rate.
Is This Answer Correct ? | 0 Yes | 0 No |
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
what is principal of pressure transmitter?
How to convert milliampares into flow??
what is function of DCS , and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
modbus and profibus communication difference?
what is cems analyzer explain with principle and drawing ?
how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?
What is profibus?
What is a snubber circuit?
what is the difference between DELTA-V & FOUNDATION FIELD BUS
In apron feeder how TPH is calculated?
how can i calibrate I/P converter