How to convert farad to kvar.
both are the unit of capacitor.
Answers were Sorted based on User's Feedback
Answer / jack
a var is a unit of reactive power
a farad is a unit of electric capacitance
see convert-units.net
Is This Answer Correct ? | 60 Yes | 23 No |
Answer / mgr
Var=VVWC
Where V=Supply voltage
W=2*3.14*F
F=frequency
C=micro farad.
Is This Answer Correct ? | 56 Yes | 19 No |
Answer / dan
var = reactive power, microfarad = capacitance
var = reactive current x voltage = (V/Xc) x V
var = V² x 2ЛfC
Where f = frequency (Hz)
C = Capacitance (μF)
Xc = capacitive reactance = 1/(2ЛfC)
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / cyclone1537
VARs = V²/ Xc = 2*phi*f*C
VARs =voltampere reactive
V =system voltage
Xc =capactive reactance
phi =3.1416
f =system frequency. hertz
C = capacitance, farad
Is This Answer Correct ? | 33 Yes | 16 No |
In a circuit the power factor was leading what will happen?
What do you mean by nominal ratio of instrument transformer?
i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.
why the protection turbo generators is most complex?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?
2 Answers Aditya Birla, Siemens,
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
Why capacitor bank ratting Kvar?
IN CABLE TRENCH WHY FILL UP THE SAND. AND WHAT IS THE DIFFERENCE BETWEEN OVER HEAD AND UNDER GROUND LAYING THE CABLES
Q. calculate the value of the resistor to be connected in series with a 100W; 230V lamp so that the wattage of the lamp is reduced to 35W
I want to know how to calculate the size of electricity cable in building?
0 Answers DR Engineering Services,
if our motor load is 150 amp v- kv and we want to install capacitor bank then what is the exact value of that capacitor bank that we should install?and how we calculate that
WHY RATING OF VCB NOT LESS THAN 630A