how can calculate static 3phase 4wire CT & PT operated
energy meter constant when calibrating using refference
meter suppose we have 11kv/110v PT and 30/5A CT, the meter
constant is 160imp/kwh, where meter is showing MW energy?
give me solution which constant i feed in my refference
meter for calibration of energy meter?

Answers were Sorted based on User's Feedback



how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating ..

Answer / s.ramesh babu

PT Name Plate details is 11kv/110/root3.
But Your EM name plate details is 415/110/root3.
and CT ratio is 30/5A.

Step:-1
Calculate voltage is 11000/415=26.50
Step:-2
Calculate CT is 50/5=10A.
Step:-3

Now EM multification factor is 26.50*10=265.06.

Is This Answer Correct ?    10 Yes 5 No

how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating ..

Answer / shah

This question set is prepared based on India's requirement.

Is This Answer Correct ?    1 Yes 0 No

how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating ..

Answer / k.prakashchandra

Meter constant is 100x6 =600 if ct and pt ratios are not
incorporated (see name plate).160 imp/Kwh is not the meter
constant and it is like rev/Kwh in EM meters

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Whats the difference between three phase and single phase?

4 Answers  


how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?

2 Answers  


what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm

1 Answers  


Why transformer is rated in kva?

4 Answers   L&T, NDPC,


Why current transformers are rated in BURDEN instead of VA?

4 Answers   Bhel,






why we are not giving the zone 1 trip command to the master trip relay

0 Answers  


How to calculate the Meter constant for the given Meter (by using any formula)

4 Answers   HCL, Viva,


what is the isolation transformer. what is the isolator?

0 Answers  


How much area a lightning arrestor can cover?

5 Answers  


difference between high and low impedance BUS BAR relay??

0 Answers  


why HT voltage rating in multiple of 11

12 Answers   ISRO,


In what way does the variable ratio-arm improve the usefulness of the wheatstone bridge?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)