how can calculate static 3phase 4wire CT & PT operated
energy meter constant when calibrating using refference
meter suppose we have 11kv/110v PT and 30/5A CT, the meter
constant is 160imp/kwh, where meter is showing MW energy?
give me solution which constant i feed in my refference
meter for calibration of energy meter?
Answers were Sorted based on User's Feedback
Answer / s.ramesh babu
PT Name Plate details is 11kv/110/root3.
But Your EM name plate details is 415/110/root3.
and CT ratio is 30/5A.
Step:-1
Calculate voltage is 11000/415=26.50
Step:-2
Calculate CT is 50/5=10A.
Step:-3
Now EM multification factor is 26.50*10=265.06.
Is This Answer Correct ? | 10 Yes | 5 No |
Answer / shah
This question set is prepared based on India's requirement.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Meter constant is 100x6 =600 if ct and pt ratios are not
incorporated (see name plate).160 imp/Kwh is not the meter
constant and it is like rev/Kwh in EM meters
Is This Answer Correct ? | 0 Yes | 3 No |
Whats the difference between three phase and single phase?
how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
Why transformer is rated in kva?
Why current transformers are rated in BURDEN instead of VA?
why we are not giving the zone 1 trip command to the master trip relay
How to calculate the Meter constant for the given Meter (by using any formula)
what is the isolation transformer. what is the isolator?
How much area a lightning arrestor can cover?
difference between high and low impedance BUS BAR relay??
why HT voltage rating in multiple of 11
In what way does the variable ratio-arm improve the usefulness of the wheatstone bridge?