how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / marcin
Equation with power factor in is the most correct. Several
issues shall be counted before estimating no load current :
- number of the poles
- power factor - there is a curve from the manufacturer
showing how this is changed in a function of power
- size of the machine
- speed
- way of feeding machine - DOL / inverter
Example :
500kW machine 690V 750rpm In=670A, No load - 285A (~42%)
500kW machine 690V 100rpm In=520A, No load - 180A (~34%)
Answer :
KW = 1.732 * V * I * cos phi * K
where K is a factor taking all other circumstances (0,7 to 1
where 1 is ideal situation) lower K for higher number of
poles, multispeed machines, specific construction etc...
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / r. n. sharma
Torque of a rotor depends on its diameter and weight along
with winding as well as material and methodology of
construction and also on applied bearings and lubrication. A
bulky, heavier rotor will draw more no load current than
small, light weight rotor. Formula : Torque (T) = qr (Where
q=Tangential force acting at PCD of winding due to effect of
current flowing through it, and r= distance of winding from
centre of the shaft). This torque only tries to rotate the
dead weight(W) of the rotor on no load. It can be said
T=qr=(W + rolling friction in bearings + wind resistance).
These all factors can be calculated easily and then finally
to arrive the result i.e. no load current, however bearing
frictional force and wind force can be ignored.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishna
normally in KW p=vicos(phi)
if we have the value of (phi)...
then using power triangle method we can find kva and from that we can find our required answerthat is no load current
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / darshana sharma
At no load 30 kW, 3 phase electric motor will draw 30% to
40% of full load current.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vaibhav
There are many factors that decide no load amperes. Material characteristic of winding material, slip of motor, voltage applied, air gap between stator and rotor, motor bearing condition etc. Mostly rewinded motors show high no load ampere sometimes up to 70-80% of full load ampere. There is no thumb rule to calculate it and in case of new motor no load ampere value is generally mentioned on motor name plate.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / janardan
For 2 pole motor; No load current will be the 1/3 of the Full load current.
i.e if motor takes 181.00 full load current then the no load current will
181 X 1/3 = 60.33 amp.
* for 4 pole: 1/3 to > 3/8
for 6 pole: 1/3 to <1/2
for 8 pole: 1/3 to 5/8
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / kailash vashisth
there is no such standard formulae but after a lot study i
found that for below 5 Hp motor Its 30% of full load
current and above 5 Hp its 45 to 50% of full load current
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / watson
i think the no load current is
Root 3 times of Full load current
i.e
I nl = 1.732 X I fl
Is This Answer Correct ? | 2 Yes | 16 No |
if the supply frequency increases what happens to the motor load
I am selected in OCL(Orissa cement Limited), but they have a Tech PI round their at their plant.Anybody has any idea that what kind of questions they are going to ask??Please guies help me. I am in serious headache.I have heard that huge elimination is done at there.
what are the different types of transformers in present? which transformer is efficient?
what's burden resistor, why it's used?
Why only plate(copper) Earth pit given for neutral earthing? why not pipe(G.I) Earth pit?
Can you explain the phase displacement between primary and secondary of power transformer of any vector group(for ex)?
what gas is present in incandescent and florescent bulbs
how to calculate busbar size? ex:11000kva main what is the busbar size ?and how to select the correct one
single phase can run in PVC conduit. Three phase can also run in one PVC conduit. But two phase cannot run in one PVC conduit. WHY? reply plz....awaiting your answer.
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
which strater used genearalyy???and why???
What is the function of NER and NET?
0 Answers Asian Paints, GHH RAND,