generally on the roadside v hav 11kv line which is being
step down to 440v line to line....so any1 can tell me which
type of transformer they r using whether it is star to
delta,delta to star etc...???
Answers were Sorted based on User's Feedback
Answer / indra bhushan kumar
high voltage side should be connected in delta ,while low
voltage side in star because in star connecton,a ground or
neutral can be fecilitated
Is This Answer Correct ? | 31 Yes | 3 No |
Answer / kranthi
IT MUST BE DELTA STAR..i.e.,on the meter side they require
415/1.732 V voltage with neutral point
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / shahulsnfa
see in delta minmum potential difference is 440. but in
star 440 as well as 230 is available. focusing in consumer
side the distribution transformer will have delta in
primary and star in secondary.
Is This Answer Correct ? | 13 Yes | 3 No |
The transformer is Delta - Star connected Transformer i.e.,
11kv is given to Delta connected side and 440v is given to
Star connected side of the transformer.
Delta side dont have neutral, while transmission neutral is
not needed.if neutral is used totally 4 wires have to be
used otherwise 3 wires are enough. 440v side we give to
homes, there a neutral is need so connected in star.
in Delta side line voltage = phase voltage. so 11kv voltage
is same.
homes need the voltage of 230v, in star the line voltage is
not equal to phase voltage. line voltage is 440v and phase
voltage is 230v.
so the transformer needed is Delta-Star
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / prithvi narayan sinha
While in Star connection we can reduce the line voltage by
57.7% due to the fact that we get the line voltage as 1/sqrt3
of the phase voltage ,hence reduction becomes easier and
convenient too. while in delta we get the line voltage=
phase voltage.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajkumar
11 kv side delta connection and 440 v side star connection
bcos delta have no nutral so no need to run 4 runs of cable
need only 3 runs. in 440 v side we need nutral so it
connected in star connection.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / arsenal
i think delta is used in the lv side bcoz in star
connection the voltage phase value will be greatly reduced
as such current is greatly increased so a large conductor
has to be used for transmission which increases the cost
and other losses.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sabale.dnyanehswar@gmail.com
generally it will be 1.1 kv/0.415kv step down star -delta
transformer.
Is This Answer Correct ? | 3 Yes | 22 No |
for 644KW load which MCCB should i use
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
what is the procedure for cable sizing or on what basis we will calculate the size of cable?????
how to find transformation ratio of squirrel cage induction motor
what are the 4 rules to start the motor?
What is the drawback of class b amplifier?
what types battery chargers are there?wanted with details.
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
what is the difference between core & shell type transformer ?& where we use those transformers ?
Is it possible to use AC supply insted of DC supply in trip coil operation? if not, why?
tell 2 reasons for why only copper is used in domestic wires& only alluminium in transmission lines ?
What is the minimum distance between taransformer (say 2000 kva)and its earth pit?