Answer / ram niveth
offcourse we can use it if we didnt consider the clock
position ie, phase displacement in primary side.
but the condition is Neutral should not be earthed in
primary side .secondary neutral must be earthed
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / karthikeyan
definetly you should reconfigure your primary winding of
the Y/Y to D/Y as per requirement. or else you have to
brought out the neutral point of primary starwinding of the
now existing Y/Y transformer.Hence you can avoid unbalance
3 pashe current by availing neutral star point which will
balance the system. and one morer thing is that you should
earth the star point of the primary winding.
| Is This Answer Correct ? | 4 Yes | 10 No |
Answer / dolphinopera
in transformers the
starting and finishing
end of the phase
windings are brought
out. hence you can
connect the windings
either in star or in
delta. another
important thing, if the
star winding is used
without neutral there
is a possiblity of
damage of winding.
| Is This Answer Correct ? | 5 Yes | 12 No |
if AVR fails in alternator. what will be the effect.
What is hysteresis losses?
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
How a band pass filter is constructed?
CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?
What is the difference between circuit and network.
15 Answers Jadavpur University, Sail, TCS,
How RTCC works with OLTC
what is (+) and (-) in generator field detector stand for?
what is power factor?
8 Answers Adani, Blue Star, Power Control,
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,
Input power is 380 - 450 V but with 45 - 55 Hz frequency - desired output is 415 V and 50hz with 1% variation permissible. CVT / Servo dont stabilize the Frequency - what is best solution??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)