WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE
(XLPE)?

Answers were Sorted based on User's Feedback



WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / c.satheeshkumar

1.For earthed and un earthed XLPE cables, the IS 7098 part2
1985 does not give any difference in specification. The
insulation level for cable for unearthed system has to be
more. In simple statement the manufacturers states that 11
KV earthed cable is suitable for use in 6.6 KV unearthed
system.The process of manufacture of cable is same. The
size of cable will depend on current rating and voltage
level.

what IS specifies and I quote below:

" b) Voltage Grade (Uo/U)

1) Earthed System - 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV,
12.7/22 kV and 19/33 kV.

2) Unearthed System - 3.3/3.3 kV and 11/11 kV.

Note 1 - Cables of 6.35/11 kV grade (earthed system) are
suitable for use on 6.6/6.6 kV (unearthed system) also.

Is This Answer Correct ?    44 Yes 4 No

WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / ajay patel

Basically, Power Systems are defined as Earthed System,
Resistive Earthed or Un-Earthed System.

Hence, Cables are designed for Earthed & Unearthed Power
System. For Example, 11 kV (E) cable is used for 11 kV
Earthed System & 11 kv (UE) cables are uded for 11 kV not
effectively Earthed System. Insulation Thickness is more of
11 kV (UE) cables compare to 11kV (E) cables.

Is This Answer Correct ?    40 Yes 9 No

WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / ashim sarkar

I fully agree with the comments of Mr. C. Satheeshkumar.
Insulation level for Unearthed system is root over 3 times
the insulation level for Earthed system.
Earthed system - Insulation of 19 KV for 33 KV system
Unearthed system - Insulation of 33KV for 33 KV system

Is This Answer Correct ?    14 Yes 0 No

WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / karthikeyan.s

For an earthed power system, phase to phase voltage is
equal to line voltage and phase to earth voltage shall be
VL/1.732. But for an unearthed power system, phase to earth
voltage shall be equal to line voltage (VL). Hence for an
unearthed system the cable insultation should be very high
to withstand the abnormal voltage during fault.
That is why it has been widely said that 6.6kV unearthed
cable shall be used in 11kV earthed application, since the
insulation level for an unearthed cable is very high
compared to earthed cable.

Is This Answer Correct ?    11 Yes 0 No

WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / b. ramachandra rao

Cables of 6.35/11 kV grade (earthed system) are
suitable for use on 6.6/6.6 kV (unearthed system) also.

But is it true other way as well?

Can Cables of 6.6/6.6 kV grade (unearthed system) are
suitable for use on 6.35/11 kV (earthed system) also.

Is This Answer Correct ?    4 Yes 2 No

WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?..

Answer / kalyan chekuri

I have a system which had 400kV 100 MVA/11 kV 50 MVA/11kV 50
MVA transformer whose secondary is earthed with NGR of 300
Amps. I have bought 18000 Km of 11 kV earthed cable to lay
on 11 kV side of it. If the phase to earth voltage is 6.4kV
and root 3 times is the voltage expected to go up i.e 11kV,
why cant it be used if the power frequency withstood for
17kV for 5 minutes

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

In case of 3 phase motor why it is called single phasing by failure of one phare unless there is rest two phase are acting. ?

3 Answers  


if a.c supply is given to the motor,, what happen?

0 Answers   Bhel, L&T, MSEB,


what is power factor

5 Answers   Exide,


What is the difference between switch gear and control gear ?

2 Answers   QU,


working of diesel generator ?

0 Answers  






what is the minimum pay scale for electrical engineer (building construction)in kuwait? plz revert back with yrs of experience & pay scale respectively.

0 Answers  


why the neutral of power transformer is always earthed?

1 Answers  


what is the procedure for three phase motor differential relay testing can it do with single phase test kit?

1 Answers   ABB,


what is the permissible bend in the LT& HT CABLES.

2 Answers  


Does voltage and current can be seperated?

2 Answers  


what is closing resistor in circuit breaker? why it used?

3 Answers  


what is x'mer ,isolation x'mer & yltra-isolation x'mer?????

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)