Answer / gova
Hi
In our substations,tan delta tests were carried out on
transformer Bushing.This test is done
1)To ensure the dielectric strength of insulation or
2)to predict the life of bushing.
what they are doing is they are measuring the capacitance
values.If the capacitance values are good means insulation
is good.
regards
gova
Is This Answer Correct ? | 77 Yes | 7 No |
Answer / sivaraman.s
the factor called 'dielectric dissipaton factor' s commonly
called as tan delta. this test s conducted not only to
predict the aging of bushing but also to predict the
contents of contaminants like soluable varnish, resins of
transformer oil.
Is This Answer Correct ? | 18 Yes | 8 No |
Answer / natarajanramkumar
Tan-Delta also called loss angle OR Dissipation factor
testing is a diagnositic method of testing cables to
determine the quality of the cable insulation.This is done
to try to predict the remaining life expectancy and in
order to prioritize cable replacement and/or injection.It
is also useful for determining what other tests may be
worthwhile.
Is This Answer Correct ? | 29 Yes | 20 No |
hello friends
tan delta test is test about reveal the aging of about
Transformers , Bushings , Rotating machines , Reactors
Tan delta and capacitance both we are measured
capacitance reveals the aging of paper insulation and Tan
delta reveals the loss factor
we are applying 2,4,6,8,10 KV for more then 20kV Equipment
Is This Answer Correct ? | 12 Yes | 4 No |
Answer / raj
before doing tan delta test, just we know that its for
determine the condition of insulation to the equipments.and
it has more benefits when compared to meggering(IR).megger
means to find insulation only behinds surface condition.but
for tan delta/dissipation factor/loss factor/power factor
is to determine internal void conditions, and their
capacitances.
permissible limits of tan delta for all bushings - 0.7%
then important one while testing of tan delta, we should
take the current test temperature, then correct that one to
20*c. . .
for that correction we should take the values from the
correction table that we do by using specific testing kit.
for megger make,doble,eltel we have different tables. just
refer and correct it.
impt: it will be compare with factory reports only after
correction of values to 20*c
Is This Answer Correct ? | 3 Yes | 1 No |
This test is doing for bushings of high rating CVT
transformers .this is very essential test it should be in
determined value max in nanofarad.whwn u conduct this one
to three times clean the bushing.this have many provision
when u using special kit.max GST-g mode is using by
applying 10Kv.
Is This Answer Correct ? | 8 Yes | 7 No |
Answer / kunal
ten delta is measurment of loss angle measured( during
testing for transformer oil) in terms of power factor
Is This Answer Correct ? | 3 Yes | 8 No |
What is Mvar?how significant is in electrical energy transmission?
why the blede and jow of isoletor demage in substation?explan.
How will you explain transformer action in case of 3-phase induction motor?
why voltage drop if we have connected 230 v ac suplly through diode to bulbe we found haft ie 110 voltage drop why it is
Why 3 over-current and 1 earth fault relay is used on primary side of transformer? Why 2 over-current and 1 earth fault relay in used on secondary side of transformer?
why the earth pin is thicker than other pins in a plug? If it is for reducing resistance, then why the copper earth wire is not so thick as earth pin of socket?
How can we save electrical cost i.e switchgear, wiring, conduiting etc in a room?
wht factor are considered to design ACB( air Circuit reaker) 415V
what is mean by xlpe swa pvc
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel
why nutral and earthing wire connect with each other in main panel board.?
Stator of 3-phase IM has 3 slots per pole per phase. If supply frequency is 50 Hz, calculate the speed of rotating stator flux A 1000 rpm B 500 rpm C 1500 rpm D 1440 rpm