Answer / sathish n p
Take an example let tr rating is 2500KVA, 11KV/415v
TO calculate maximum loading on primary side
2500 X 10^3=1.732 X 11 X 10^3 X I
I=131.01Amps
Similarly Secondary side
2500 X 10^3=1.732 X 415 X I
I=3478 Amps
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / debashis
For determining the optimum loading of a transformer we need
to determine the load for which my copper loss would be equal to my iron loss.
At this point the loss would be at its minimum level and hence
the efficiency would be maximum.
Remember Iron loss is independent of load and copper loss depends on the load.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / elminshawy
Sorry Vikadeny
But how it is optimum if I bought a 100MVA transformer and
I only loaded it to 50MVA or 70MVA ?
for optimum loading of transformers please refer to IEC
standard (60354 Loading guide for oil-immersed power
transformers )
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajendran
I think question refers to the optimum loading at which the
efficiency of the transformer is more/maximum...
if it is like that then we can refer the loading curves
provided by the manufacturer of the transformer....
generally as a thumbrule the optimum loading point is
around 85 to 95 percent of the capacity..
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vikadent
As a rule of thumb, the optimum loading is between 50% to 70
% and my reference is Electrical installation guide by
Schneider and this is the range where the losses are minimum
inside the transformer.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / khalid hussain shaikh
POWER=1.732*VOLTAGE*CURRENT*POWER FACTOR
HERE POWER=2500KVA
VOLTAGE=11 KV
POWER FACOR AS STANDARD=0.85
I=?
I=2500KVA/1.732*11KV*0.85
KV CANCELLED EACH DENOMINATOR AND NUMARATOR,
I=2500/1.732*11*0.85
I=154 AMP (11 KV SIDE)
I=2500 KVA/1.732*415 V*0.85
V CANCELLED EACH DENOMINATOR AND NUMARATOR
I=2500 K/610.963
I=4.091 KA
I=4091 AMP
| Is This Answer Correct ? | 10 Yes | 16 No |
How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.
How does cost of generation from hydropower plant compare with other sources of electricity?
What are the Full Forms of TVM, MTL, CVT ?
why HT wire making noise?
what is open star connection or open delta.
WHAT IS VCB SAFETY
What kind of Neutral CT can be placed in 11/0.433KV transformer to be used and what are its specification?
what is the use of Antipumping in HT breakers.
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
what is LT & HT?
How many types of timer ?which timer are used star delta feeder
When motor stater and roter air gap do big then what will moter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)