In a three phase transformer(delta/star connected)when i
touch one end of the bulb in any one phase and other end to
earth..will the bulb glow or not..if not why?..i'm touching
the bulb in star connected side...
Answers were Sorted based on User's Feedback
Answer / jagjeet
If it is distribution transformer and having 440 line to
line voltage , definately bulb should glow because the
bulb has been connected via earth i.e. 220 volts ( Phase &
Earth)
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / arockia doss
Bulb will glow.
Since, The req. voltage for the bulb will be coming from
the phase.
The neutral will be coming from the Earth.
Becuase, In the star connected trf. the neutral will be
earthed & So that, the bulb will glow.
Thanks ...
A.Arockia Doss
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / vinay sangwan
This question is not complete because star side voltage is
not specified.
| Is This Answer Correct ? | 7 Yes | 7 No |
Answer / vksumith
secondary(star connected) phase voltage is 110v and line
voltage is around 230v..
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sachin rana
bulb will be glow if transformer is properly earthed i.e body as well as neutral
| Is This Answer Correct ? | 0 Yes | 0 No |
If the field winding of the dc shunt motor is removed then what will happen to the motor ? will it turn or not
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
can I connect step down transformer(25KvA,240V Phase to phase)to output of online UPS(15KvA,440V PHASE TO PHASE) Load connect to TRANSFORMER is 13KvA,240V PHASE TO PHASE. please brief if it is wrong
size of condotory fron voltage level
Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?
why the air gap is necessary in the transformer core
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
what is the purpose of the armored for the power Or control cable? How to select the type of the armored?
difference between silent and non silent pole rotor?
The principle of switching circuits for different types of batteries in application of storage systems
how to detect the presence of underground cable(while digging road)etc. -give the name of instrument
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)