Answer / ankamsreekar
The effective capacitance is 3 time more in delta as
compared with star connection provided that same capacitors
are used.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / sreenu
Becasue, in delta connection,voltage of three phases is
equal and the power factor( Reactive power)is depends on
voltage.
If you use star connected capacitors, the voltage may vary
due to unbalenced loading of capacitor whcih is indirectly
depends on load.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / dr. shahid
In delta the effect is 3 times as compared to when they are star connected.
Regards
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jonathan r. lambert
Capacitors are paralleled with inductive (magnetic) loads
in delta, wye (aka "Star") and single phase AC power
sources to correct power factors so that motors,
transformers and other inductive loads appear to be
resistive. Power factor correction is a process that
cancels reactive current vectors leaving only a resistive
current. Inductive loads pull currents that contain both
resistive and reactive vectors. In power factor correction,
a capacitor's reactive current is used to cancel the
inductive reactive current created by magnetic coils in
inductive devices. If the capacitor is sized correctly the
current drawn by the capacitor will precisely cancel the
inductive magnetization current pulled by an inductive
load. The resulting motor current "seen" by the AC voltage
source will then be only resistive. Since power companies
charge for both reactive and resistive current, and since
only the resistive current is required to provide
horsepower and perform work, power factor correction
reduces the current drawn by inductive loads which reduces
the electrical operating expense. Hard to believe that
applying an additional parallel load, a capacitor, will
result in less total current but it works due to the
capacitive reactive current leading at +90 degrees and the
inductive reactive current lagging at -90 degrees, the two
parallel currents sum at the voltage source to equal zero
degrees and if the cap is sized correctly, zero amplitude.
| Is This Answer Correct ? | 3 Yes | 13 No |
what is the difference b/w neutral and earth?what is the need of earthing and what are the different methods for earthing?
what is difference bwt active&passive component
What is the following which is printed on electrical appratuses like AC21 ,AC 23 , etc ?
what is the location of lighting switch of battery room
Differenciate between circuit wiring and sub main wiring with illustrations
what is merz price protection
ouestion for the post of section engineer
how instantanious short circuit current is calculated ? its formula.
As per principle we say in three phase supply ,the voltage is producing by phase angle between two phase so two phase is needed means then why we using three phase ?
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
While testing a ZCT what parameters have to check or measure?
what is the slip of synchronous motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)