phase clearance between phase to phase and earth
Answers were Sorted based on User's Feedback
Answer / s pradhan
For 11 KV;Ph-Ph-130 mm
Ph-E -100 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
Is This Answer Correct ? | 54 Yes | 19 No |
Answer / geetha
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
for 11 KV : Ph-Ph-229mm
Ph-E-178 mm
for 11 KV : Ph-Ph-229mm
Ph-E- 178mm
for 33 KV : Ph-Ph-320mm
Ph-E-320mm
for 132 KV : Ph-Ph-1100mm if Lightning impulse = 550
Ph-E- 1100mm
Ph-Ph-1300mm if Lightning impulse = 650
Ph-E- 1300mm
for 220 KV : Ph-Ph-1900mm if Lightning impulse = 950
Ph-E-1900 mm
Ph-Ph-2100mm if Lightning impulse = 1050
Ph-E-2100 mm
Is This Answer Correct ? | 28 Yes | 10 No |
Answer / saleem
phase clearance between phase to phase and earth in
11Kv,33Kv and 66kv System.
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / mathi
ans: 110mm for phase to earth
130mm for phase to phase
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sinnadurai sripadmanaban
Please give clearances for indoor as well as for outdoor and in air/vacuum/SF6 or within a switchboard(enclosure-IP..)
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / bmw6633@gmail.com
phase to phase 1inch and for earth 1 1/2 inch
Is This Answer Correct ? | 11 Yes | 25 No |
How to calculate cable size by using load.?? Any formula...
ABOUT AC GENARETORS AND MAINTANANCE AND TYPES OF GENARETORS
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
CAN ANYBODY PL TELL ME WAT FACTORS CAN CAUSE UNDERVOLTAGE ON A BUS??? PL LIST ALL THE REASONS WITH SOME EXPLAINATION
ii) A shunt motor supplied at 230V, runs at 900 rpm when the current is 30A. The resistance of the armature is 0.4 ohms. Calculate the resistance required in series with the armature to reduce the speed to 600 rpm, assuming that the armature current is then 20A. [12]
How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?
What is PQA???Applications........
HOW BETTER VOLTAGE REGULATION IS OBTAINED BY HIGH VOLTAGE TRANSMISSION....?
What is different between resistance grounding system and resistance earthing system?
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
what is the difference between the characteristics of two different phase bushing of any transformer
what is the minimum winding resistance of 30hp compressor, to run or to switch on