why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit kumar singh
The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).
As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / d.lakshmi narayana
To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load
Is This Answer Correct ? | 1 Yes | 1 No |
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
What is the use for cable entry in control room?
Can we transmit digital signal to long distance ?
What is sinusodial & non sinsodial current
What are the classification of Servo Motor?
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
i have to use generator in my project,which gen. i can use?
how we can check new PT ? without name plate.
1 Answers Indo Power Projects,
what is pure resistive circuit and pure inductive circuit
How do you select a cable size(cu and Al) for a particular load
what is the meaning of Air condition "TON"
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?