why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit kumar singh
The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).
As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / d.lakshmi narayana
To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load
| Is This Answer Correct ? | 1 Yes | 1 No |
Is MEN and RCD related to each other ?? IF yes then how??
Why air circuit breaker off due to power failure?
what is the principle of operation of CFL ??
what's the use of cvt and wave trap in 400kv switch yard.......
whu does the power factor of diesel generator always be 0.8. please explain
when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?
what is the relation between knowing of the distance between power transformer and the capacitor feeder in case of parallel operation
Which type of power plant is more easier to produce electrical power at economical condition?
How to calculate Ith (I thermal) for curent transformer
State magnitude criterion.
What is an alternator impedance value?
in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)