how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / shubhabrata sengupta
Chiller IKW/TR
Chiller Rating - 650 TR
Power Consumption – 100 KW
IKW/TR = Consumed Power in KW / Generated chiller TR.
Chiller is running at 34% i.e. 221 Generated chiller TR
Therefore IKW/TR is 100/221 = 0.45
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / balram singh mnadloi
TR= (delta T*flow)/(3.5*0.86)
and
KW=(1.73*V*I*PF)/1000
Then you have to divide TR by KW so you find Ikw of chiller
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shashi
Halo guyz,1TR =3.5KW is not electrical power .it is thermal unit .So don't confuse
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashok
1TR --- 3.5KW
1kw ----8633btu
1TR -----12000BTU
1kw/TR --- 1.396
| Is This Answer Correct ? | 24 Yes | 26 No |
Answer / puneet prashar
As we know that 1 KWh = 3413 btu ( British thermal
unit)But not 1kw, but it is = 8633 btu
and 1 TR = 12000 btu
kw capacity = 12000/8633
Hence 1 TR = 1.39 kW
| Is This Answer Correct ? | 6 Yes | 14 No |
Answer / jitendra patel
IKW in HVAC = (Chilled water TR x 3025)/860
for example Hvac = 200Tr
Ikw = 200*3025/860
=703.48
| Is This Answer Correct ? | 17 Yes | 29 No |
what is lowest system voltage?
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3
hi frienda We have 750kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
Why using synchronising methed in DG's sets?
what condition there autotransformer will fail?
how to prepare the technical test
Dear all, kindly give me the details of leectrical design engineer course details/institute in hyderabad /any where in india.
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
FEINGING DECREASES THE FLUX DENSITY IN THE AIR GAP. HOW?
How to generate neutral in DG set?
why inverter rating is in KVA
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)