how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / nilantha warushavithana
1 TR = 12,000 BTU/h
1 BTU/sec = 1.055 kW
12,000 Btu/h = 3.5166 kW
1 kW = 3412.3 BTU/h
Is This Answer Correct ? | 14 Yes | 1 No |
Ikw
Power input in kw for per ton of refrigeration KW/TR
FOR EXAMPLE 100TR CHILLER
FOR PRODUCING 100TR POWER CONSUMED 90 KW
IKW /TON = 100 / 90 = 0.9 i.e 0.9 KW /TON
to find IKW,COP,EER
If the power consumption is 1 kw /ton power consumption
system will provide cop of 3.5 and EER will be 12.
Is This Answer Correct ? | 17 Yes | 7 No |
In general Practice you can consider 1 Tr = 1200 Watt = 1.2
kw
1 TR = 3.5 KW is next to impossible.
Is This Answer Correct ? | 35 Yes | 26 No |
Answer / sohal
to find out ikw
Amp.X Volts X Power-factor X 1.732/1000= kilowatts
then divided by machine tonnage = input kilowatt(IKW)
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / sandip bharne
1Tr=80x907/24 ( ice requires 80kcal/hr to melt,907 is US
short ton)
=3023 Kcal
1kw= 860kcal/hr
1TR =3024/860
1TR =3.51KW
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / carol
Be Carefull!!!!
TR and W are POWER UNITS
Btu is an ENERGY UNIT
As everyone knows from Basic Physics:
Energy = Power x time
The actual conversions are:
12.000 Btu/h = 1 TR
1 TR = 3517 W
Therefore,
12.000 Btu = 1 TR-h
12.000 Btu = 3517 kWh
Watchout!!!!!.....
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / shri narayan gond
I know that 1 kw = 3413 B.T.U. and 1T.R.=12000 B.T.U. ,1T.R.=12000/3413.=3•5Kw.
Santiry fugle chiller I.K.W.=lode k.w./T.r.
For ex. My chiller capacity is 760 tr. And lode
509 kw.
I.K.W. =509/760
Ikw =0•669
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / pradip
1TR= 12000BTU = 3000KCAL = 3.516KW,It is a thermal Unit,
But IKW relate of Power Consuption of Kw/TR,
In market many HVAC systems area available,so every systems
has different IKW,
Example : for VRV system
1TR consume 0.95 to 1.2KW,
1TR=1.2KW,
so IKW =1.2
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / ruka
1TR=3.5kW <-- Cooling Capacity
3.5kW/COP = Electricity Consumption; normally COP>= 3
COP = Coefficient of Performance
If COP = 3.5
then;
1TR = 1kW <--- Can be varie
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh chavan
we need saving power consumption in HVAC system. please share
Is This Answer Correct ? | 5 Yes | 1 No |
Why two nos. un-tensioned wires are placed inside the PSC poles used by powergrid in RGGVY works.
What is difference between Over Current & Earth Fault protection?
what is current
What is the difference between Floot charge and Trickle Charge.
what is skin effect?
Whot is the braking capacity for MCCB. How we select different braking capacity.
What is power transformer?
what are the various types of towers used in transmission line
12 Answers Power Grid, UltraTech,
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
whta does the middle finger stands in flemings left hand rule
What is High Frequency Grounding????
what is the use nuetral wire