How to select Main CB Rating for 187 KW Load?
Answers were Sorted based on User's Feedback
Answer / abdulsubur
Total load =187kw
p=root3*vicosphi
i=p/root3v*cosphi
we get aprorximately 400
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ramaraj.g
Selecting main CB rating first.
187KW / votages LL
187000/400
467.5 amps this type current rating is not in market
so we will go to next rating 600 Amps
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / abdulsubur
P= Root3*vicosphi
calculate i from this equation apploximately
we can use 400A ircuit Breaker
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rajendran
Apart from the nominal operating current we have to
consider the following factors also
1) Capacity of the source
2) Fault lvel of the system
3) Breaaking capacity of the breakeer required based on the
fault level obtained..
4) Space avilable
5) cost requirements
6) Method of controls in the breaker
7) Protection facilties avilable....
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / bala
Selecting main cb rating depends on the type of load if it
is combination of small loads (upto 10kw) 400amps mccb is
enough.
1. if it is one motor load. first we have consider what
type of starter we are going to use. in case of star delta
starter select 600amps mccb. in case of VFD and softstarter
400amps mccb is enough.
Is This Answer Correct ? | 4 Yes | 3 No |
what you have to see after one week or month from the day of installation of transformer ?
How many electrones need to flow in one second to equivalent to one Ampere.
What is the role of the 50 STUB protection at a GIS 400KV substation with SIEMENS protection relays?
what is hormonics. how it is generated & what are the problem faced by that.
What type of motor is used inside computer CPU.
State kirchoff voltage law?
What is the battery voltage limit
The transformer which is smallest in size is and how to calculate that? The options are 100 KVA, 50 Hz 100 KVa, 100 Hz 100 KVA, 25 Hz 50KVA, 25 HZ
4 Answers Ranbaxy, Zee Laboratories,
What is A check, B check, C Check & D check for a diesel Generat
0 Answers Jtekt Koyo Bearings,
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
how squirrel cage & slip ring motor works? how they differ from each other
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition