what should be the value of proper neutral earthing
resistance?
Answers were Sorted based on User's Feedback
hai i am saravanan from madurai ( west masi street )
answer:
below one ohm should be maintain in neutral earthing.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mahesh sali
for solid earthing it will come around - 5 ohms
for resistive earthing the value being 1 to 2 ohms
for reactance earthing the above value will come down
around , it will be les than 1 ohm ,
thank u
Is This Answer Correct ? | 6 Yes | 0 No |