what do you mean by earth fault in transformer?
Answers were Sorted based on User's Feedback
Answer / shailesh aggarwal
Basically Earth faults are caused if high fault current
flows through the neutral of the transformers. This type of
fault arises mainly in Star connected transformers.Earth
faults are specified in many categories:
1. Restricted Earth faults(Inside the zone HT/LT side of
trafo) Connection are done b/t Phase CT & Neutral CT of
tranformer)Indicated as REF(64)
2. Standby Earth Faults(Directly linked with neutral of
trafo)connection only done b/t neutral CT.Indicated as SBEF
(51N).
Both the protection give signals to the numerical relays
and cause the tripping as earth faults and directly trip
the transformer.
Thus in order to save transformers a proper earthing is
required whether solid or usong NGRs.
Is This Answer Correct ? | 22 Yes | 2 No |
Answer / nilkanth tailor
EARTH FAULT REQUIRE C.T.(CURRENT TRANSFORMER)..TO SENSES
IMBALANCE IN 3 PHASE..GENERALLY 3PHASE SYSTEM IS IN BALANCE
CKT...IF SINGLE OR MULTI PHASE WAS EARTHED..AND AT THAT
TIME IMBALANCE PRODUCED..CT WILL BE DETECT FAULT CURRENT
AND CIRCUIT BREAKER WILL BE OPEN...THATS CALLED EARTH FAULT
PROTECTION OF X'MER...
Is This Answer Correct ? | 9 Yes | 6 No |
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
why characteristics of overcurrent relay is time-->psm instead of time-->current?
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
how work the differential protection relay in details?
wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .
Calculate torque developed by the 3-phase, 5 H.P., 4 pole induction motor runs at 1500 rpm A 23 N-m B 21 N-m C 10 N-m D 0 N-m
why reactor is connected before capacitor in APFC panel
a 3 phase slip ring induction motor is wound for 4 poles on stator and 6 poles on rotor; when 3 phase balanced voltage source at 50 hz is applied to motor it will run at a)1500rpm b)1000rpm c)750 rpm d)zero rpm
13 Answers Essar, PSPCL, PSTCL,
how does bode plot have an advantage over root locus? how does it determine the stability of a system depending upon the location of poles and zeroes?
In protection core of a C.T. why Knee pont voltage is greater than SLV and in metering its viceversa?
how do u get less voltage in star connection
why should we connect the no load components in a equivalent circuit of transformer in parallel?why cant it be in series.