Why generating power limited to 11kv?
Answers were Sorted based on User's Feedback
Answer / 7anoter4
There are generators of which supply voltage is up to 30 kV
[usually 22-23 kV for 500-800 MVA].The problem is the
insulation- will be very expensive for higher voltage-the
generator it self and the auxiliary switchgear and
transformer. A medium voltage generator and a step-up
transformer is cheaper and more convenient for maintaining.
Is This Answer Correct ? | 17 Yes | 4 No |
Answer / rahul anand
The generating
capacity of
power plant is
given by
multiple of form
factor(1.11)
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / abdul muneeb khan
ABB research
http://www.abb.com/cawp/seitp202/c1256c290031524bc12567310024e1e4.aspx
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / chyray
that are no limit on generating "Voltage"
e.g. Singapore HT network system are 22Kv, so standby
Generator are 22kv or 415v at LT side.
BTW generating power unit are "KVA" or "MVA" not voltage.
Is This Answer Correct ? | 0 Yes | 6 No |
How to PLC give the command to electrical
in basic 2 phase will short means tripping the power but spot welding 2 phase shorting but not tripping it will welded why.....(Q)
Which system is best for industries 3ph 3w or 3ph 4w?
what is the difference between equipment earth and system earth.
What are protections for dty type transformers
What is the basic principle of welding process?
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
in the exciter the power is feeded from battry or control or whatever.and we need it in the generators for the stating . do we need it in the shutdown also?i mean the exciter>
Do you know the faults occurs generally in motors and how to rectify them?
Why neutral grounding Transformer provided for generator?
what about electrical pannel.? What is meant by plc pannel.?
Why grounding is generally done in supply end?