What do you mean by pf of a generator? Power factor purely
depends on the load (wether inductive, reactive or unity)
then what does the pf mentioned on the generator nameplate
means?
Answers were Sorted based on User's Feedback
Answer / madhusudhan
Kw= 1.732X Voltage X Current X pf. in these parameters only
current and pf are variable. The current limitation given on
the DG set is at that pf. if pf increases the current will
get decreased for the same KW. so you should monitor the
same pf as mentioned of DG set name plate or else you should
reverse calculate the current limitation at your load pf and
monitor the DG set no to get overloaded.
| Is This Answer Correct ? | 5 Yes | 2 No |
I try this,
see,power factor is the percentage of resistive load in the
total circuit.as the power factor is one it indicates the
pure resistive which is real in number which can be
converted to the what ever the real energy we want like
rotatory motion etc...
frm:rajeshbeesetty@yahoo.com
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / balajieee
power factor is the cos angle between voltage¤t.using
that nameplate pf value u can find kw capacity of a
generator for its kva rating(formula,p=sqrt3*v*i*cospi.).if
you are connecting pure resistive load means power factor
is unity,so the pf of generator will incrase from its name
plate value.capacitive load also incrase the pf of
generator.inductive load will decrease pf value.so the
average of resistive,inductive,capacitiveload pf ,name
plate pf will give final output pf of generator.
| Is This Answer Correct ? | 3 Yes | 13 No |
What are the basic components of the feedback control system?
How good are you in resolving the commercial issues to Employer's advantage?
On Which Pressure PRV is operated.
how to make parrallal ups
6. A DC AMMETER HAS R=0.1 OHM & CURRENT RANGE IS 0-100 A IF THE RANGE IS TO BE EXTENDED TO 0-500 A THEN METER REQUIRES SHUNT RESISTANCE OF ..........
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
What is the ampereage of .75 ton Ac
how to select rating of HT Panel
How do we check transformer losses and what are the ways to minimise it.
I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)