Why is making current of CB always greater than CB breaking burrent?.
Answers were Sorted based on User's Feedback
Answer / john henry
Making capacity is the MAX current that a CB can pass at
the occurence of fault.
And breaking capacity is the RMS value of current at which
CB can break its contacts open.
Now when fault occurs, system goes into the subtransient
state and a huge amount of current flows in the system.
and this time if the breaker is reclosing and the making
capacity is low it will burn so it is high.
Breaking is low so that it can be isolted from the system
as soon as the fault occurs with less arching and to save
the contacts of the breaker.
Is This Answer Correct ? | 35 Yes | 3 No |
Answer / gunasekaran
breaking current is always rms value making current are peak
current. because at the fault condition breaker will be re
closing at sub transient condition. at subtransient
condition current is more so the designed making current
value is less it will burn. so making current always more
than breaking current. it is about 2.5 times of breaking
current.
Is This Answer Correct ? | 16 Yes | 3 No |
Answer / aqeel
Making current implies dc component so it is 2.5 times
breaking current
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / palani
The CB breaking current is less than Making current. The
breaking occur at the zero of the alternating Current where
as making occur at any amplitude of current in the
alternating current .
Is This Answer Correct ? | 20 Yes | 18 No |
Answer / sudar
Which one more save opening CB at capasitive or inductive
condition???
Is This Answer Correct ? | 2 Yes | 8 No |
Answer / sagar hingmire
Bcoz If making current capacity is not greater than
breaking current then if fault is there on electrical
system & ur going to close CB then very high fault current
will flow through CB and CB will get damaged or blast as
fault is not cleared.
Is This Answer Correct ? | 6 Yes | 18 No |
The capacity of the transformer is 20/25 MVA, Ratio is 132/11 KV, Vactor group YNyno. and impedance is 10.07%. As per the calculation the secondary current is 1312.2Amps. The maximum fault current the transformer should sustain is 13.030KA. How many times the transformer should sustain the maximum short circuit current of 13.030KA over a period up 1 Year. The transformer is repaired one & 10 Years old.
why is the transmission voltage is multiple of 11?
what is the meaning of electrical maintenance?
3 Answers GE Healthcare, MAHINDRA,
What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?
we have 1000 litre water tank,it located at 25m hight from ground level,the water level on 10m below from ground level.for fill the tank within 1 hour,how much of motor rating(HP) want to select?
Why we are using only Dyn11 tranformer in distribution system but not using a Dyn1 in distributing system?why not and advantage and disadvantage in both
how does oil cools the transformer
How DC to AC convert
what is the use of the puls transformer in UPS & how it works???????????
Safety of on line ups
0 Answers Bhushan Power Steel, GE,
what is a power factor?
0 Answers MPWU Kiribati, Thermo,
What is size 00, 01, 1 etc., in HRC fuse types?