Why is making current of CB always greater than CB breaking burrent?.

Answer Posted / palani

The CB breaking current is less than Making current. The
breaking occur at the zero of the alternating Current where
as making occur at any amplitude of current in the
alternating current .

Is This Answer Correct ?    20 Yes 18 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Starting Time of LT & HT Motor

1488


WHAT IS SUBSTATION & ACCORDING TO VOLTAGE HT,EHT SUBSTATION EXPLAIN IT

2695


how to select correct size of power cable for inverter duty motor

925


How to convert 2 phase to 3 phase electricpower in induction moter?

1682


Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?

2889






how to calculate voltage drop and followed by cable calculation?is there avail in formula?

1592


What is the Current equation in series RLC circuits.

621


Which contains in POLE ASSEMBLY of a 11KV Kirloskar-make SF6 (Model No-FP620A12)? Will u clarify with drawing?

1754


100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.

1846


what is your majour contributions in your present job

1344


kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased

2155


what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??

2116


when the time of backcharging the transformer three phases only enough or three phase with neutral is must.from these which one is the best one.

1583


how to find the resistance and gap volatage of the diode??

1559


What is difference between isolator and circuit breaker?

626