Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is the impact of MCCB & MPCB on Distributed Control
System?

Answers were Sorted based on User's Feedback



What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / kasi

MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.

Is This Answer Correct ?    12 Yes 5 No

What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / manish rane

MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.

However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection

Is This Answer Correct ?    9 Yes 2 No

What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / pyobik

MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.

Is This Answer Correct ?    9 Yes 3 No

What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / avinash yashwant gunjal

MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A

Is This Answer Correct ?    6 Yes 1 No

What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / avinash yashwant gunjal

MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.

MCCB for protection of distribution system.

MPCB,
overload ,short circuit protection for INDUCTION MOTOR

Is This Answer Correct ?    4 Yes 0 No

What is the impact of MCCB & MPCB on Distributed Control System?..

Answer / harris

How to install ZCT and what is the funtioning for MV Motors?

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure

0 Answers   APTransco,


Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB

0 Answers  


What is process of anneling transformer core

0 Answers  


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel

4 Answers  


If o/p power is doubled by how much does the sound increase

0 Answers   Flipkart,


what is the formula or method to calculate RESIDENTIAL,COMMERCIAL & INDUSTRIAL load power?????

3 Answers   RRB,


how can we chacke adiod in a circuit

2 Answers  


what is the abbreviation & meaning of UI charges

1 Answers   MNC,


Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?

1 Answers  


Stator of 3-phase IM has 3 slots per pole per phase, calculate number of stator pole pairs. A 1 B 6 C 2 D 3

2 Answers  


What is relation between mu(nought) and epsilon(nought)?

0 Answers  


Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)