What is the impact of MCCB & MPCB on Distributed Control
System?
Answers were Sorted based on User's Feedback
Answer / kasi
MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / manish rane
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.
However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / pyobik
MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / avinash yashwant gunjal
MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / avinash yashwant gunjal
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.
MCCB for protection of distribution system.
MPCB,
overload ,short circuit protection for INDUCTION MOTOR
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harris
How to install ZCT and what is the funtioning for MV Motors?
Is This Answer Correct ? | 1 Yes | 1 No |
why swinburnes test cannot be performed on series machines?explain
How does one convert an AC motor into a generator?
Piezoelectric materials serve as a source of:- A. Microwaves B. Ultrasonic waves C. Musical waves D. Resonant waves
i have to use generator in my project,which gen. i can use?
What is the need for a controller?
the parts of transformers ?
1 Answers Bhel, Facility management,
Comment on the working principle of operation of a single-phase transformer.
what are the difference between AC lamp and DC lamp
what is effect of 5amp fuse on 2mva pry protection of transformer
WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW