What is the impact of MCCB & MPCB on Distributed Control
System?
Answers were Sorted based on User's Feedback
Answer / kasi
MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / manish rane
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.
However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / pyobik
MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / avinash yashwant gunjal
MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / avinash yashwant gunjal
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.
MCCB for protection of distribution system.
MPCB,
overload ,short circuit protection for INDUCTION MOTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harris
How to install ZCT and what is the funtioning for MV Motors?
| Is This Answer Correct ? | 1 Yes | 1 No |
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
What is process of anneling transformer core
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel
If o/p power is doubled by how much does the sound increase
what is the formula or method to calculate RESIDENTIAL,COMMERCIAL & INDUSTRIAL load power?????
how can we chacke adiod in a circuit
what is the abbreviation & meaning of UI charges
Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?
Stator of 3-phase IM has 3 slots per pole per phase, calculate number of stator pole pairs. A 1 B 6 C 2 D 3
What is relation between mu(nought) and epsilon(nought)?
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)