Answer / iamdon
No,Transformer efficiency measured with the help of
wattmeter can't be reliable.
The reason is
The efiiciency of transformer is very high (order of 98.5-
99+)% due to static nature of it.The error associated with
ordinary wattmeter is in the range of 1-2 % .Under this
condition the readings taken cann't be reliable.
The efiiciency is measured with the help of data taken from
two tests namely
Open circuit test--indiaction of core loss
Short circuit test--indication of copper loss.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / dabangg
NO . TRANSFORMER READING IS IN KVA SO WEW CANT TAKE A
READING IN WATTMETER
Is This Answer Correct ? | 0 Yes | 3 No |
In VVVF drive voltage is varying in accordance with frequency.My question here is How much will be the voltage in the inverter side if the frquency is set for 10Hz ?
What is on line ups and off line ups?
Why front mounted CT polarities are always towards breaker?
Define ampere
What is difference between safe PLC and normal PLC
In the UVR(Under Voltage Relay) there is a knob for the hysteresis setting. what is this setting? its threshold is given from 5% to 50%. please help me....
Our transformer capacity is 500kva & voltage ratio is 11kv/433v step down tf.Now i need to know if my input voltage is 10500v and what would be the secondary side voltage i.e output voltage ?
when we connect the capacitor bank in series
Differentiate between Low and High impedance Protection
Why shunt Generator is not recommended to start at ON LOAD condition???
what is timing for mccb 800A tripping?
What effect of supplying stationary generator (800kVA) with 415V AC from 1500kVA transformer?