sir, plz tell me how much kvar capacitor required for 1000 
amp or 500 Kw load ? what is the formula ?
 Question Submitted By :: Electrical Engineering
  I also faced this Question!!      
Answer Posted By  
 Answers were Sorted based on User's Feedback
# 1
Formula : KVAR = KW(tanĂ˜1-tanĂ˜2) 

Is This Answer Correct ?    33 Yes 10 No
# 2
Dear Shovan
This is Prakash veer
According to madhu's formulas,

KVAR= KW* (tanQ1-tanQ2)

Q1 is intail power factor
Q2 is target power factor 

Is This Answer Correct ?    19 Yes 3 No
prakash veer singh
# 3
we need power factor value 

Is This Answer Correct ?    14 Yes 4 No
# 4
Required data for calculation your demand KVAR

1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)

KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering 

Is This Answer Correct ?    8 Yes 2 No
santosh maske
# 5
kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.

Is This Answer Correct ?    7 Yes 3 No
# 6
Madhu pls explain what is tanphi1 and tanphi2???? 

Is This Answer Correct ?    5 Yes 1 No
# 7
25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken

1000amps capacitor required to 500kvar 

Is This Answer Correct ?    4 Yes 1 No
# 8
250 Kvar Capacitor bank is required for 500Kw load
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load 

Is This Answer Correct ?    7 Yes 5 No
malkit singh
# 9
plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2) 

Is This Answer Correct ?    2 Yes 0 No
saleem iqbal
# 10
Reactive power (KVAR) is increase due to run inductive a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.

active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR

so we have to use 300KVAr capacitive capacitor bank to remove this reactive power . 

Is This Answer Correct ?    1 Yes 0 No
bijoy roy

Other Electrical Engineering Interview Questions
  Question Asked @ Answers
Why we use neutral cable just half from phase cable.Tell me briefly,please.   4
what is the function of CRGO in a Transformer?   6
in 400 kv system why should trip both side CB when we give hand trip? nhpc 1
why we are caling 440 volt 3 phase supply instead of 660 volt 3 phase supply? because each phase as a voltage of 220 volt. if anybody know the answer for my question please send it to my mail id. thank you. nec 3
as we see that in our country the power rating for transmission is always rated in multiple of 11 like 11kv,33kv,66kv132kv. So i want to know wht is reason or logic here.   1
what is FET   1
why we somewhere use ryb phase sequance, somewhere use uvw, and somewhere abc??   4
when secondary volts is given how do we find primary volts, turns, amps of primary and secondary given???   1
Why is the earth pin in a 3-pin plug the longest and the thickest? ibm 10
Which type of DC generator is used for electric welding purposes and why?   1
explain me the exact concept of generator neutral....????   2
For more Electrical Engineering Interview Questions Click Here