sir, plz tell me how much kvar capacitor required for 1000
amp or 500 Kw load ? what is the formula ?

Answers were Sorted based on User's Feedback



Answer / madhu253

Formula : KVAR = KW(tanĂ˜1-tanĂ˜2)

Is This Answer Correct ?    35 Yes 10 No

Answer / prakash veer singh

Dear Shovan
This is Prakash veer
According to madhu's formulas,

KVAR= KW* (tanQ1-tanQ2)

Q1 is intail power factor
Q2 is target power factor

Is This Answer Correct ?    19 Yes 4 No

Answer / arun

we need power factor value

Is This Answer Correct ?    14 Yes 4 No

Answer / santosh maske

Required data for calculation your demand KVAR

1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)

KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering

Is This Answer Correct ?    8 Yes 2 No

Answer / deepak

kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.
SO POWER FACTOR IS REQUIRED.

Is This Answer Correct ?    7 Yes 3 No

Answer / shovan

Madhu pls explain what is tanphi1 and tanphi2????

Is This Answer Correct ?    5 Yes 1 No

Answer / elangkumanan

25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken


1000amps capacitor required to 500kvar

Is This Answer Correct ?    5 Yes 1 No

Answer / malkit singh

250 Kvar Capacitor bank is required for 500Kw load
(i.e,625Kva).
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load

Is This Answer Correct ?    7 Yes 5 No

Answer / saleem iqbal

plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2)

Is This Answer Correct ?    2 Yes 0 No

Answer / bijoy roy

Reactive power (KVAR) is increase due to run inductive load.as a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.

active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR

so we have to use 300KVAr capacitive capacitor bank to remove this reactive power .

Is This Answer Correct ?    1 Yes 0 No


Post New Answer

Categories
  • Civil Engineering (4339)
  • Mechanical Engineering (3608)
  • Electrical Engineering (15283)
  • Electronics Communications (2597)
  • Chemical Engineering (545)
  • Aeronautical Engineering (78)
  • Bio Engineering (30)
  • Metallurgy (94)
  • Industrial Engineering (188)
  • Instrumentation (2782)
  • Automobile Engineering (132)
  • Mechatronics Engineering (40)
  • Marine Engineering (58)
  • Power Plant Engineering (144)
  • Engineering AllOther (1303)







More Electrical Engineering Interview Questions

explain the what is a drive ? 0 4 which type motor r use in the celling fan..... PCB plannet 2 13 If stator & rotor of a 3-phase induction motor have different no. of poles, will the motor run or not?? types of drives Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups ac supply only. ACC 1 41 how the 3phase induction motor is running in 2phase supply with help of capacitor? 1 33 what is the actual difference betwen constructional details and constructional features? 1 20 how does commutator convert a.c to d.c?

0 Answers  


What is the List of Equipments, Instruments, Components required in Transmission of electricity from 1 substation to other substation(The equipments required in substation too)? What are the differnt IS standrds used for above equipments in Industry?

2 Answers  


Ceiling Fan and Storage type water heater. Discuss

0 Answers   Satyam,


HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?

5 Answers  


how to check dc current,how to fix ammeter in dc line

5 Answers   Gold Fields,


Why in india freq. is 50HZ & in U.S.A. it is 60HZ?

2 Answers   MacLellan,


234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,

0 Answers   Jubail O&M,


i want to know how to determine that a surge arrester work properly in 11kv system. and how to test a 12kv surge arrester

0 Answers  


What will happen if i replace a inductive proximity switch with photo sensor in a machine?

0 Answers   Hitachi,


can we use inductor for passing or blocking of AC or DC?

3 Answers   NTPC, Moser Baer,


what is the difference between Inverter and ups

1 Answers   L&T, MTS,


wheather the size of windings in motor and generator are the same

0 Answers