sir, plz tell me how much kvar capacitor required for 1000
amp or 500 Kw load ? what is the formula ?

Answers were Sorted based on User's Feedback

Answer / madhu253

Formula : KVAR = KW(tanĂ˜1-tanĂ˜2)

Is This Answer Correct ?    35 Yes 10 No

Answer / prakash veer singh

Dear Shovan
This is Prakash veer
According to madhu's formulas,

KVAR= KW* (tanQ1-tanQ2)

Q1 is intail power factor
Q2 is target power factor

Is This Answer Correct ?    19 Yes 4 No

Answer / arun

we need power factor value

Is This Answer Correct ?    14 Yes 4 No

Answer / santosh maske

Required data for calculation your demand KVAR

1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)

KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering

Is This Answer Correct ?    8 Yes 2 No

Answer / deepak

kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.

Is This Answer Correct ?    7 Yes 3 No

Answer / shovan

Madhu pls explain what is tanphi1 and tanphi2????

Is This Answer Correct ?    5 Yes 1 No

Answer / elangkumanan

25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken

1000amps capacitor required to 500kvar

Is This Answer Correct ?    5 Yes 1 No

Answer / malkit singh

250 Kvar Capacitor bank is required for 500Kw load
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load

Is This Answer Correct ?    7 Yes 5 No

Answer / saleem iqbal

plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2)

Is This Answer Correct ?    2 Yes 0 No

Answer / bijoy roy

Reactive power (KVAR) is increase due to run inductive a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.

active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR

so we have to use 300KVAr capacitive capacitor bank to remove this reactive power .

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

  • Civil Engineering (4378)
  • Mechanical Engineering (3622)
  • Electrical Engineering (15337)
  • Electronics Communications (2598)
  • Chemical Engineering (565)
  • Aeronautical Engineering (78)
  • Bio Engineering (30)
  • Metallurgy (94)
  • Industrial Engineering (189)
  • Instrumentation (2799)
  • Automobile Engineering (132)
  • Mechatronics Engineering (40)
  • Marine Engineering (58)
  • Power Plant Engineering (146)
  • Engineering AllOther (1306)

More Electrical Engineering Interview Questions

What are the role of each components in PID COntroller

1 Answers   BARC,

what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?

0 Answers  

How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????

6 Answers   Emerson,

why dc source used for HV breakers and Relays operation?

2 Answers   Cethar,

Currently what is the highest capacity (MVA) of SPPg generator available in the market?

0 Answers   SPPG,

why does chattering take place in ac contactors? can it be avoided & what care does the manufacturer take to eliminate this phenomenon????

8 Answers  

How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.

1 Answers  

What is stray current in DC Traction?

2 Answers   L&T,

While testing the value of the resistance for the earthing rod, two auxillary rods are connected to the earthing tester.What is the working function of a earth tester?

0 Answers  

how does an energy meter works?

4 Answers  

which one is more costly:single phase induction motor or 3 phase induction motor??give proper reasons..

1 Answers  

how to calculate singlephase motor efficiency?

0 Answers   Alstom,