what is mean by marshalling box in transformer?
Answers were Sorted based on User's Feedback
Answer / k.ganesh
Marshalling box contains the following items:
i)winding and oil temp.indicators
ii)Tr.Triping and alaram signals between tr and relay,taken
through marshalling box.
thank you,
| Is This Answer Correct ? | 103 Yes | 17 No |
Answer / abduljameel
It is like box type arrangement.All the transformer
protection like winding,oil temperature,pressure alarm,are
wired upto this box for remote monitoring or to incomer relays.
| Is This Answer Correct ? | 76 Yes | 14 No |
Answer / sripellirajukumar
ya
this is rajkumar from one of the reputed power transfomer
manufacturing company
as u said above is wrong
actually the marshalling box used with the transformer is
contains one WTI(winding temparature indicator) OTI(oil
temparature indicator)and few connectors (these r some
connecting devices like plugs to give the normal operating
voltage to the WTI and OTI from external supply).from this
box only we can abserve the condition of transformer..and we
will operate the relays and ckt breakers manually or
automatically depends on the fault condition.....
thanks,,,,,,,,,,,,,,
| Is This Answer Correct ? | 73 Yes | 11 No |
Answer / tufail
Marshalling box is a type of box which is connected at one
side of transformer. It consists of WTI(winding temperature
indicator) and OTI(oil temperature indicator). WTI are in
two numbers, one for HV and other for LV. It consists of a
heater which is used to absorb the moisture in the box.
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / haha
before going to subject topic .At first we have to know what is meant by marshalling ?(It means arrangement) Hence Marshalling box is an arrangement of protective devices like WTI,OTI etc.....through which we can observe the status of transformer
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / hiresh
In general Marshalling box is a common Junction box where
all local sensor are terminated and a common cable taken to
remote monitoring station either Substation relay console
panel [RCP] or DCS or PLC.
On the other hand in PLC /DCS also use this word, where the
different I/Os wired to terminals and from there the cables
is drawn to field sensors/equipements/instrumens.
| Is This Answer Correct ? | 16 Yes | 20 No |
Answer / varun
Marshalling box is complete with
a) 240 V, 15A, SPN socket outlet, complete with switch and
HRC fuse for hand lamp
connection.
b) Cubicle lamp (CFL) complete in all respects (with lamp
holder, switch, HRC fuses)
but without lamp.
c) All auxiliary contactors as required in the order to
make necessary potential free
contacts for remote alarm and tripping.
d) Marshalling box shall be weather proof type and shall be
provided on the front side
of transformer tank and not on radiator.
6.2 Marshalling box shall be provided with terminals for
oil temperature indicator, winding
temperature indicator, magnetic oil gauge and buchholz
relay and other control terminals as
applicable.
| Is This Answer Correct ? | 11 Yes | 15 No |
Answer / anubhav pandey
Maeshalling box is actually, a rectangular type box which consists of OTI (OIL TEMPERATURE INDICATOR), WTI (WATER TEMPERATURE INDCATOR). This inidcator indicates the current readings of Oil as well as Water. And, alarm is also associated in the respective box which start beeping when the specified temperature of water or oil exceeds or goes down. Various performance & monitoring could also be done with the help of this Marshalling box.
| Is This Answer Correct ? | 0 Yes | 11 No |
Why does amplifier gain reduce?
in how many ways we can make induction motor to run in reverse direction?
7. Hrc fuse provides best protection against.......
5 Answers SSC, UGVCL Uttar Gujarat Vij Company Ltd,
1 kva how much amps? How to calculate ?
which subject is better to tell when hr asks the area of interest?..
Is there any question in the name of Static Switch in UPS??
in conclusion why we select you?
how we can calculate LT side current of transformer
what's transient & sub- transient reactance means?
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
what happen if the battery is charged by more than one source ,for ex: connecting data cable to laptop & charger pin to source supply ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)