Answer / promise mbanga
Looking at this question from the chemistry point of view,
l can confidently say:
(i) Coal in form of graphate, is a good conductor of
electricity due to a free electron wondering around it's
bonds, hence the resitance of earth reduces due to the
presents of coal.
(ii) Salt in solution for does ionise to Na+ and Cl-
ions. These ions are good conductors of electricity, hence
the earth resistance does reduces when salt is present on
earth.
(iii) Water does partially ionise to give H3O+ and OH- ions
which conduct electricity. This also reduces the earth's
resistance.
| Is This Answer Correct ? | 35 Yes | 2 No |
the hard water is one of the good conductor of elecricity
as explained in ship earthing.
the mixing of these things in earth makes the earth
conductive n hence reduces the earth resistance.
| Is This Answer Correct ? | 21 Yes | 3 No |
Answer / gkumar
Hi,
Both coal & salt acts as good conductor of electricity .
also when they are mixed & put in the earthing pit they
provide conductivity as well as moisture for better passage
of current
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / p mishra
Coal are the form of graphite which is a best conductor.So
for reducing the earth resistance we use coal.Like salt is
made of Na+ Cl-.These ions are good conductors of
electricity, hence the earth resistance does reduces when
salt is present on earth. Water conducts partially. So all
the materials when mixed the resistance/ohmic value is
reduced.
| Is This Answer Correct ? | 2 Yes | 0 No |
If the positive terminal of batteries in 125 v dc system is connected to earth what will happen ?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?
What are linear and non-linear systems?
Merz-Price circulating current principles is more suitable for
Why in celling fan stator are rotatig while rotor are steday
what is CT class? depending upon which it is classified?
How to set an overload in a motor?
what should be the value of proper neutral earthing resistance?
why dc series motor high speed motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)