If the positive terminal of batteries in 125 v dc system is
connected to earth what will happen ?
Answers were Sorted based on User's Feedback
Answer / stugger
hey nothing will happen, i dont know the technical reason
for this but i have tried for the 192 v dc battry sytem and
there is no shrt ckt.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / sathish
This case is almost like a short circuit. Voltage almost becomes zero. And the current flowing becomes maximum
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / vinod
1) In ungrounded system nothing will hapend, earth leakage
information display in battery charger.
2) In -ve grounded system short circuit occur and
protection will operate with annunciation.
Normally ungrounded system is using with
leakage detector
| Is This Answer Correct ? | 4 Yes | 0 No |
Nothing wil happen, such system are adopted in
Telecommunication power supply since its inception and may
be for avoiding over voltage due to positive nature noise
added in the circuit. Always there will be less voltage
that (-) 125 Volt when any (+) volts noise is added.
| Is This Answer Correct ? | 1 Yes | 0 No |
Can we loop AC neutral wire with DC neutral wire?
if we want to convert the two 12 V DC batteries in parallel for UPS ? what would be the result ? which is better for a UPS , connect two batteries in series or connect them in parallel ?
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
A 100 MVA transformer may be cooled with?
In the UVR(Under Voltage Relay) there is a knob for the hysteresis setting. what is this setting? its threshold is given from 5% to 50%. please help me....
if the 10 hp motor name plate indicates rated current as 13.6 amp the what will be the thermal relay setting? Why? And in how much time relay will trip at the set value?
how can calculation ate Amps for cabel. Ex-for 1sqmm wire hou many amps we can draw
i need about 10 years of GATE solved papers in pdf format and even mock tests toooo
State magnitude criterion.
WHY IS THE SIZE OF HOLE OF THE EARTH POINT IN THE PLUG POINT BIGGER THAN PHASE AND NEUTRAL
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
What is earth?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)