how can we can take BDV test in transformer?

Answer Posted / ilononurb

we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.

Is This Answer Correct ?    78 Yes 8 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439

542


why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.

1542


how can we change the phase angle b/w two phase?

4086


What is pi controller?

666


What is meant by vector group

1976






Please define ohm’s law for a.c (alternating current)?

642


we have 15 ampere variyac but we want 30 ampere variyac what we do

1418


What happen Grid EARTH plat got cut.

1744


What is transmittance?

640


How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.

1725


we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?

1489


According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.

3693


we are going to install a solar PV site and how can we calculate PV Solar Panel Efficiency, can anybody tell me complete method for its calculation.

1575


what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable

1527


why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.

1522