Suppose am having the PF value .8, so how can we say that
is it lagging or leading?
Answers were Sorted based on User's Feedback
Answer / raveendran.p
Pf is usually spelt as 0.8 lagging or 0.8 leading. There is
error in telling otherwise. However relatively 0.8 can be
assumed as lagging since lagging pf is commonly encountered
in power systems. Leading pf mostly will be stated
explicitely.
| Is This Answer Correct ? | 29 Yes | 1 No |
Answer / mukund
if you are considering any equipment such as motor or
lighting load such as fluorescent lights
most of the loads are inductive in nature
you are talking about 0.8 lagging p.f.
people are using capacitor banks to improve p.f. upto unity
in this case it is definately 0.8 lagging p.f.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / vidhya
THE NATURE OF A POWER FACTOR WHETHER ITS LEADING OR LAGGING
IS DETERMINED BY THE TYPE OF LOAD WE ARE CONNECTING TO THE
SYSTEM.
| Is This Answer Correct ? | 13 Yes | 1 No |
POWER FACTOR
1.If the value is -0.8 then it is lagging pf.
2.If the value is +0.8 then it is leading pf.
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / gunasekaran
normally load r lagging nature so it is lagging power
factor only
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / nandu
Raveendran.p is right
if insufficient data is given than it is assumed to be lagging.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / priya
if generator burden increases with this pf it is said to b lag and vice versa is lead
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / santoshvarma
Just is the KVAR value from multifunction meter if it is
positive then 0.8 is lagging pf and if the KVAR value is
negative then 0.8 is Leading power factor.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / manoharmadhu kumar
by taking the avarage values of kwh and kvah . by
considering this values we can say that if kvah is greater
it is -0.8 pf or if kwh is greater it is +0.8 pf or if both
values are same it is unity pf or it is=1 pf .
by manoharmadhukumar
| Is This Answer Correct ? | 0 Yes | 2 No |
Is it advisable to buy a plot for house construction near High Tension Power lines? If it so how much distance it should be away from power line? Iam residing at Chennai, Tamilnadu, India.
srij i need the relationship b/w KW AND KWH and with an electrical example. plz send if u can?
Air circuit breaker safety
Is 2000kva stabilizer suitable for 1h.p split air conditional
What is the function of auadag in a cro?
Reason of secondary of ct always short
In separately excited m/c,we excite the field by a dc source,what not with ac source?
why the secondary current transformer cannot left open
How two nos. 130 kw D.C motor get synchronise using D.C drive.
How the frame size of a flange mounted AC induction motor is calculated?
what is the requirement regarding earthing of Single conductor with AWA
We have given to 3phase supply to ups system & how can coming netural
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)