How to calculate unit consumption on the basis of load.
kWH=kwXhrs.is it correct? kw is motor load.What is unit
consumption at 100% load, 50% load & on no load.
Answers were Sorted based on User's Feedback
Answer / satish m
For three phase motor we needs to consider the PF also.
P = Sq.Rt 3 X V x I x pf
| Is This Answer Correct ? | 62 Yes | 8 No |
Answer / shannu
Unit consumption is KW x Hrs.
But while you need to calculate the KWH consumed by a motor,
multiplying KW of motor (nameplate KW) and hour will not
give you the energy consumed. This is because the name plate
KW in a motor is not the electrical power, but the
mechanical power output provided by the motor (Electrical
Power = Frictional losses + Eddy current losses + Copper
losses + air gap losses + Mechanical power). In order to
calculate the energy consumed by the motor you can use the
formula
single phase AC = Voltage x Rated current x Power factor x
Hrs run. (100% load)
3 Phase AC = 1.732 x Voltage x Rated Current x Power factor
x Hrs run. (100% load)
Normally the power factor of motor is considered between 0.8
to 0.85 at full load operation.
At no-load, motor will take approx 40% of its rated full
load current (again this depends on the design of motor, but
normally assumed to be near 40%). So at 50% load, the motor
will take a current around 70 to 75% of its full load rated
current. so we can approximate as
energy consumed at 50% load (motor - 3 phaase) = 1.732 x
Voltage x 75% rated full load current x power factor x Hrs run .
at no load = 1.732 x Voltage x 40% of rated current x power
factor x Hrs run.
| Is This Answer Correct ? | 32 Yes | 7 No |
Answer / shivpal prajapati
kwh=kw*hrs is not correct.
kw=1.732*v.i.0.85,if motor rated current 64amp,
Then calculated value kw=1.732*415*64*0.85
| Is This Answer Correct ? | 26 Yes | 9 No |
Answer / sakil belim
i have 70 hp 3 phase load. I run 70 hp in 1 hour in perday
what is kwh
| Is This Answer Correct ? | 22 Yes | 8 No |
Answer / tushar amarghade
for 100% load
unit(kwh)- kw*hours/1000
where,
KW for single phase- V*I*PF
KW for THREE phase- 1.732*V*I*PF
| Is This Answer Correct ? | 4 Yes | 1 No |
Capacity of circuit breakers all types
why we use end termination kit for ht xlpe cables
what is safety measures of alternator.
10 Answers HP, MNC,
how we can calculate earth fault current?
HOW COULD A SINGLE PHASE INDUCTION MOTOR ROTATE IN OPPOSITE DIRECTION???
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
What is the difference between Neutral And Earth ?
State the points to be considered for selecting a particular type wiring.
can we use relay in fan?
What is main purpose of chock coil and starter in florescent tube ?
Two bulbs of 500w and 200w rated at 250 v will have resistance ratio as ?
2 Answers CGL, Dreamz Infra, Sunny Developers,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)