what is the principal of star delta starter?
Answers were Sorted based on User's Feedback
Answer / sayan
The pinciple of a star dela starting is based on the fact
of reduction of the starting current at the time of
starting of the motor. But there is always a surge of
current whenever there is a transition from star to delta.
This is essentially useful for the motors which are
connected to systems which are prone to have a voltage dip
at the starting of the motor.But the only disadvantage of a
star delta starter is that the starting torque reduces
appreciably during starting the motor in star.
Is This Answer Correct ? | 111 Yes | 13 No |
Answer / shyam prakash ray
The principal is to keep the starting current in safe limit
so that the motor achieves 70% of speed as connected to
star side, since the motor draws very high current at the
time of starting due to high starting torque.
Once the motor gets started then it is changed/converted
into delta side either manually or automatically for
running.
Is This Answer Correct ? | 32 Yes | 7 No |
Answer / ravinder kashyap
work of a starter is reducing high starting current
in star connection voltage is Vph=Vl/root 3
so at starting time of motor we are use star connection at
starting star connection are use then after picking normal
speed after this delta connection are applied to motor
this is the principle that by use of star /delta voltage
conversion scheme
Is This Answer Correct ? | 25 Yes | 5 No |
Answer / amit vishwakarma
Star delta starter used for squirrel cage motor,utilises the principle of reducing the starting voltage.all the six terminals( each of two) of 3 phase induction motor are brought to the starter ......
In fact start delta starter is simply a two way switch. The method is based upon the principle that with 3- winding connect in star, the voltage across each winding is 1/√3..i.e.57.7% of the line to line voltage whereas, the same winding connected in delta will have full line to line voltage across each.
The star delta starter connects three stator winding in star across the rate supply voltage at the starting instant. After the motor attain speed, the same winding through a change over switch are connected in delta across the same supply voltage..
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / guru
TO REDUCE THE STARTING CURRENT FOR SERIES MOTORS.
Is This Answer Correct ? | 12 Yes | 8 No |
Answer / ernest parku
Star is to reduced the high starting torque of the motor or the high surge current to a full load of delta connection.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ganesh ghule
The pinciple of a star dela starting is based on the fact
of reduction of the starting current at the time of
starting of the motor.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / guna sekhar
induction motor draws 4times the load current of motor intially. so we use star -delta starter to reduce intial current . first the windings connected in star thereby reduces the intial current by 1/../3[root3].after certain time delay its converts winding connection to delta.
Is This Answer Correct ? | 6 Yes | 8 No |
Answer / ketan
Reduction starting curernt because of current is devided in
phase 60%.
Is This Answer Correct ? | 11 Yes | 15 No |
In three phase energymeter the spindle rotating backward why?
what is the value of current as well as voltage upto which we will not feel shock and why?
700KW 6.6KV slip ring induction motor to use VFD to control the speed
Haw to check conductivity of budbar
what is bus pt and what is the function of it ???
pleasee tell me the risks and hazards of a Cable Jointer job? Thank you.
ouestion for the post of section engineer
difference between substation & grid substation?
hi this is hema can anyone mail me previous years questions for the APPSC-A.E.E (in electrical stream.) ......thank u.
What will be the effect of in HT XLPE 220 KV cable when one side of the Armour/cable ends are not grounded. Will there is difference between 3-phase voltages? like: if A. Both End of Cable grounded Phase Voltages:- V1=219 KV, v2=220 Kv, v3=220 KV. B. One End is grounded other is not: than Impact on Phase Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or unchanged??
In a running D.G set engine and Alternator is revolving at 1500RPM but no output in the terminal>>>>what to do?? someone told excitation problem ....please advice
how do i get electrical supervisor certificate in gujrat?
3 Answers DGVCL Dakshin Gujarat Vij Company, Infosys, ONGC, Orient, Reliance,