WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER?
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER?
Answers were Sorted based on User's Feedback
Answer / jagadisha
The vector group is used to know the type of winding in
Transformer.First letter in the vector group indicates
primary winding(neutral is indicated if present) and the
second letter indicate secondary winding and next letter is
indicate phase difference between primary and secondary..
let us consider vector group Dyn11-It is most coomon 3-PH
connection,ie Delta is on primary and Star on sec with phase
displacement of 30deg
| Is This Answer Correct ? | 19 Yes | 10 No |
Answer / bijay
well things are explained well above.
i wud like to add something
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER ?
Ans:-First thing under an abnormal condition(during fault)
the neutral point of trafo rised above the ground potential
and attains a positive potential,hence a current will flow
through the trafo neutral to the ground (mostly the trafo
neutral is earthed with or without a NGR.
As a whole the bottom line is trafo neutral will rise to a
potential which is not desired,protection against the same
is designed,which cut of the supply it this condition
prevails for a longer time( this time is descided at the
time of designing the system.
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / sunil ulange hit nidasoshi
Vector Groups are made especially to make out difference in
the connections. The connection can be delta(D) or star(Y)
The primary winding connection always denoted by Capital
Letter (D), and secondary winding connection always denoted
as small letter (y), and neutral n
The number after that indicates the phase difference
between the primary and the secondary voltage.
e.g.-> DYn11 means transformer is star connected with
secondary voltage leading the delta connected primary
voltage by 30 degrees.
normally distribution transformers are have Dyn11 connection
because secondary of transformer are connected to at user
end means motors,inductive load etc,
These loads always havelagging Power factor thatswhy Dyn11
connected transformer means secondary volatage leads by
primry voltage by 30 degrees, hence Power factor maintened
constant.
In Clock 11 indicates angle between 12 & 11 is 30 degrees
i.e. 360/12=30 degree
Sunil ulange
Application Engineer
Southern power equpment Limited bangalore
any Questions @ sunil_031@yahoo.com
| Is This Answer Correct ? | 16 Yes | 11 No |
Answer / poonam
Vector Groups are made especially to make out difference in
the connections. The connection can be delta(D) or star(Y)
The number after that indicates the phase difference
between the primary and the secondary voltage.
e.g.-> Y11 means transformer is star connected with
secondary voltage leading the primary voltage by 30 degrees.
I am not sure of the effect of phase displacement in
transformer
| Is This Answer Correct ? | 16 Yes | 12 No |
Answer / geno peter
well , significance of vector group depends upon the load
of the transformer. if phase displacement changes then the
connections in the transformer or tap switch of the
transformer has some problems
| Is This Answer Correct ? | 2 Yes | 7 No |
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
what happens if earth of 33kv cable is not connected to earthing pits? please send this query's answer to ngrm.sudha249@gmail.com
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
what is the chemical name and formula of refrigarent R-134a.
What is the significance of %Z in case of transformer?
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
what is name of transformer oil ?
58 Answers L&T, MPSEB, OPTCL, Practical Viva Questions, Servo, TATA, XLPE, ZGL,
what is the difference between electrical choke and electronic choke?
tan delta test of current transformer.
How to calculate cable sizing
We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)