WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER?
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER?
Answer Posted / jagadisha
The vector group is used to know the type of winding in
Transformer.First letter in the vector group indicates
primary winding(neutral is indicated if present) and the
second letter indicate secondary winding and next letter is
indicate phase difference between primary and secondary..
let us consider vector group Dyn11-It is most coomon 3-PH
connection,ie Delta is on primary and Star on sec with phase
displacement of 30deg
Is This Answer Correct ? | 19 Yes | 10 No |
Post New Answer View All Answers
difference between semiconductor & conductor & insulator?
What do you understand by avr?
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
How to calculate mf when meter equipment and meter are connected
How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.
how to calculate single phase motor efficiency ?
Which level of the Transformer oil got dielectric strengh? And why?
State the methods of improving power factor?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
what is induction furnance? how many phase supply given io its coil for 15 or 20 ton furnance?
What descriptive information does the NEC require to be marked on all conductors?
how ceiling fan worked?
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??