How we check vector group for a Dyn1 transformer?
Answers were Sorted based on User's Feedback
Answer / s.ravindra
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / gunasekaran
we can find out from ratio kit
if applied UV-vn get energised
if applied VW-wn get energised
if applied WU-un get energised
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / vinod maurya
We will short 1U & 2U
And we will apply 3 phase voltage between 1U,1V,1W
Measure between
1U-1V
1V-1W
1W-1U
1V-2v
1V-2w
1W-2w
1W-2v
1W-2n
2n-1U
Verify The Condition
1W-2n+2n-1U= 1U-1W
1W-2w=1W-2v
1V-2v<1V-2w
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / y.rama krishna
Connect 1U&2U
Apply 3ph 415V balanced voltage across terminals 1U,1V,1W
(HV wdg)
Measure the voltages between the given terminals & record
1)1U-1V
2)1V-1W
3)1W-1V
4)1V-2V
5)1V-2W
6)1W-2V
7)1W-2W
8)1U-2N
9)1V-2N
Verify the conditions
a)1W-2W = 1W-2V
b)1V-2W = 1V-2V
c)1U-1V = (1U-2N)+(1V-2N)
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 18 Yes | 16 No |
Answer / mahmoud moustafa
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
this is correct I check today in one of GE sites
| Is This Answer Correct ? | 2 Yes | 0 No |
what are the pecularity of shaver sockets ?
Describe the test procedure to determine the vector group
how can we change the phase angle b/w two phase?
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
Can we test the alignment of End shield and stator of turbogenerator without rotor insertion? Also how to fix maintain the alignment at site installation?
why we use copper earthing for neutral while for body GI.
1 Answers Chennai Metro Rail Limited CMRL, Valeo Lighting Systems India Private Limited,
What is derating?, Why it is necessary, it is same for all means for drives, motors,and cables.
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?
why tan delta test conducted in electrical equipmenr
why dc is used in control circuits for MV & LV switchgeras instead of ac
Safety measures in air circuit breaker
5 Answers Megatron Solutions, TCS,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)