how to calculate the capacitor rating for improving power
factor
Answers were Sorted based on User's Feedback
Answer / r n seth
capacitor required is too be calculated from required power
factor to desired power factor.the formula is-
Req. Cap in KVAr= Tr. MVA* PF( tan cos-1(existinf PF- tan
cos-1(desired PF))
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / engr. tariq
Formula :
C = P (tan|old - tan| new) divided by Omega (w) and then
divided by Voltage (RMS) or Vrms.
theta (|) can be calculated by knowing cos theta OR power
factor. Example PF is 0.77 then Cos theta = 0.77 and Cos
inverse (0.77) = 39.646 = Theta OLD. Now
Now if i want to improve PF to 0.9 then theta = Cos inverse
0.99 = 25.841 = theta New.
After calculating theta put it in the Given formula to
calculate Capacitance required.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / engbri
Another way i use is to take the PF and turn it into an
angular measurement in degrees. using j notation and the
magnitude of the wave you can calculate the size of
resistance, or real component and the size of the inductive
reactance or the -J component. Do this with a simple Polar
to rectangular conversion, if you cant your calculator
probably can. Then making the capacitive reactance equal to
the inductive reactance cancels it as they are oposites.
Then using the formula Xc = 1/2piFc transpose for c which
gives c =1/2piFXc. however as the cpacitor is taken as
ideal and with no resistive component this will never
reduce the PF to zero.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / charu gupta
kVAr Rating = kW(tan A - tan B)
Where kVAr rating is the size of the capacitor needed,kW is
the average power drawn, tan A is the trigonometric ratio
for the present power facotr, and tan B is the
trigonometric ratio for the desired PF
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / engr. tariq
Please note that in answer # 5 omega (w) is equal to the
frequency of the system.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / salman
to find above answer so we can directly go through
contract technical book this easiest way.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / pavan vyas
as a thumb rule it should be 1/3 of load kw & theoretically
we can select from the chart
| Is This Answer Correct ? | 8 Yes | 13 No |
what is L.T?specify the range?
How can get C license i am complete I.T.I electrician trade and 10 years experiance this field and i complete the dee from ksou by distance mode of this year.ksou means karnataka south open university but i want Tnelb license
Where is the center of magnetic field in alternator
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
how encoder works?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
Why is starter necessary for a three-phase induction motor?
37 Answers BMM, Essar, Hero MotoCorp, ITI, Maruti Suzuki, Supertech, Watt,
how to check avr of dg set of 125kva
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three
What is the purpose of starter and choke in tube light?
9 Answers Chimay Brewery, TATA, TSPL,
110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)