THE 40 MW OF POWER FOR 220 V III PHASE POWER CONNECTION
REQUIRES HOW MANY KVA POWEER REQUIREMENTS
Answers were Sorted based on User's Feedback
Answer / reshi
If we assume the power factor during motor running as 0.85.
Then the calculation will be 40MW/0.85= 47MVA.Answer.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / riyadh
this formula u going to apply
Kw=Kva*P.f
we know P.f = 0.9 for T/f's
P.f = 0.8 for Generator
we knw power kw 40Mw
Apply to above formula Kva = kw / p.f
Kva = 40000 Kw / 0.8
Kva = 50000 kva
In Mva is 50
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / chethan
p- 40MW,v,220volts kva=?
40*1000000*4.54Amps multiply (1000=1.732*220*I,ans.4.54)
Ans. 181600 KVA
this is my knoldge ,so this is error,please tell me the
correct answer.
Is This Answer Correct ? | 0 Yes | 0 No |
Its 50000Kva on .8 pf and answer#3 is correct.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayaraj
The question is wrong. 40MW load could not be fed from 220v 3 ph system. If the question is the KVA requirement 50000KVA on .8 pf. So in a distribution system 2000KVA Transformer 25 nos are required.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / v.s.narayanaswami
THE ABOVE FORMLA APPLIES FOR CONVERSION OF HP INTO KVA AND
THE CORRECT CONVERSION FACTOR IS 0.764.
THE REQUIREMENTS OF 40 HP CONNECTION CONVERTED INTO KVA
APPLYING THE FORMULA IE 1 HP = 0.764 KVA IS 40HP/0.764 IS
APPROXIMATELY IS 52 KVA.
HENCE UR CORRECT REPLY IS SOLICITED FOR ARRIVING AT THE KVA
DEMAND FOR THE ESTIMATED 40 MW OF POWER CONNECTION
REGARDS
V.S.NARAYANASWAMI
B.COM(HONS), M.COM, F.C.A
Is This Answer Correct ? | 2 Yes | 12 No |
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
What is the function of UV coil ACB?
is that any software calculator to calculate the size of cable
what is the thumb rule or formula for cable size and current ratings
Why at the starting of induction motor current is high?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
what the main difference of the 3 phase and 2 phase power supply??
when qty of cable being purchased is not sufficient according to the standard,what should the inspector do to ensure its quality according to the standard?
what is the difference between synchronous motor and induction motor?
describe the phenomena of vacuum interruption in C.B
How many straight through joint is permissible in single core 33kv XLPE cable for a length of 985 mtr.
Technical specification of a wind farm