Answer / arpita
Under normal operating condition m.m.f or ampere- turn
both primary and secondary oppose each other. When
secondary of C.T is open circuited then there is no
demagnetiging ampere-turn to oppose the primary ampere-turn
and therefore, the primary ampere-turns now become active
in producing a very high flux density in the core which
result in very high inductance e.m.f. in the secondary
winding.
This high induced e.m.f. is likely to cause
a) Overheating of core
b) Breakdown of insulation
c) An electric shock to the attending personnel.
For these reason secondary of C.T in power system not act
as an open circuit.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / gajanan
there are 2 possibilities
1.if we keep secondary of ct open, then only primary mmf
will be present in core which saturates the core
2.in fault condition due to high frequencu current core
saturates means permeability of core decreases very much as
good as wood
| Is This Answer Correct ? | 0 Yes | 1 No |
Define thermal resistance in the context of power amplifier.
What is the pro & con of having 11kv & 33kv incoming, and what is the adv & disadv. of converting from 11kv to 33kv.
What is FM200 Fire Supresion System??
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
How the main bus bar rating of 400kV switchyard with one and half breaker scheme is calculated.
In 63kva LT Distribution Box Why the outgoing of 63A kit kat is connected to 200 A link disconnector? as the output of kit kat is only 63 A?
What is the role of link in neutral in a three phase ac system?
what ll happen if neutral is not shorted with phases while doing transformer short circuit test & what ll happen if neutral is connected to ground?
What meant by lagging and leading? When if they are occurred what preventive methods should be taken?
14 Answers ABB, L&T,
What are the material used for resistor?
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
Write the current equation in series RLC circuits.
0 Answers Agilent, Integreon, ZS Associates,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)