what will happen if the connections of protection ct reverse?
will it burn the ct?
Answers were Sorted based on User's Feedback
Answer / sheikh
in case of reverse connection CT will not burn . however connected equipment may goes to malfunction or dead condition. as per example if Ct connected to kw meter and connection made inverse then kw meter given reading in Minus
like -245,-500kw . an other if ct work with any protection device like on reverse power relay in gen set and connection made in reverse then gen set goes on reverse power shutdown.
| Is This Answer Correct ? | 1 Yes | 0 No |
if your protection is only 50/51 there will be no effect,
but if you enable function of 32,67, and 87T, relay goes to malfuntion
| Is This Answer Correct ? | 0 Yes | 0 No |
why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
Define the term Capacitance and Inductance?
how does a liquid starter reduce the starting currents?
does not the circulating current in a transformer affect the flux distribution in the transformer core
What will happen if the 50HZ Transformer is connected with 60HZ power Supply
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
what is the abbreviation for F.M In FM-200 fire suppression system
What is a soft start?
I want formula to calculate cable size as per load given in kw & amp.I searched many sites but didn't right answer.Plz reply me asap.
41 Answers Armco, BEL, BGS, Biocon, BRB Cable, Crystalline Chemical Industries, DLF, Doshion, Electrical, Gold Roof, L&T, Lanco, MEIL, Oman Cables Industry SAOG, PK Services, Polycab, Sabic, SLV, System Electrical, Tata Motors, UEM, UMIC, Vega, Vertex, Voltas,
If the generator will not synchronize, what will you do?
Differenc between the resistance and resisters?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)