what will happen if the connections of protection ct reverse?
will it burn the ct?
Answers were Sorted based on User's Feedback
Answer / sheikh
in case of reverse connection CT will not burn . however connected equipment may goes to malfunction or dead condition. as per example if Ct connected to kw meter and connection made inverse then kw meter given reading in Minus
like -245,-500kw . an other if ct work with any protection device like on reverse power relay in gen set and connection made in reverse then gen set goes on reverse power shutdown.
Is This Answer Correct ? | 1 Yes | 0 No |
if your protection is only 50/51 there will be no effect,
but if you enable function of 32,67, and 87T, relay goes to malfuntion
Is This Answer Correct ? | 0 Yes | 0 No |
How much resistance between neutral earthing and body earthing of Power transformer?
what is cut out fuse?
1) name the communication cable and how it is communicate in between plc to modbus , plc with hmi? 2)name of the communication cables?
why the capacitors works on ac only
How to calculate the Airconditioner capacity for a standard telecom BTS shelter?
what is the chemical name for oil that used in the transformer
What is the need for a controller?
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
How to size the Neutral grounding resistor?
how will i find Transformer rating if supply voltage is 11k.v and how will i find incomer if transformer rating is 12MVA
how tubelight circuit is connected and how it works?
In a incandescent bulb, if the glass is punctured, and then power is supplied, the tungsten filament blows up with a flash.Why?