Why is starter necessary for a three-phase induction motor?
Answers were Sorted based on User's Feedback
Answer / farha
A starter is needed for a three phase induction motor
because at the time of starting, if induction motor is
started directly, it will draw large amount of current
which causes damage to adjoining equipments.
Thus, a starter is needed in order to limit the starting
current.After the motor has started at reduced starting
current and hence reduced voltage, the connections are
diverted towards the mains supply so that now, the motor
can run at higher starting current and voltage.
Four types of starting methods are employed:
1.Star-Delta
2.Auto transformer method
3.Primary resistor starting.
4.Direct On-line.
Low rating upto 7 H.P motors can be started directly.
Is This Answer Correct ? | 607 Yes | 51 No |
Answer / jessy
By starting an induction motor with starter limits the
starting current and starting torque .
Note - Upto 5 to 7.5 HP Three phase induction motors
generally started direct on line .
Is This Answer Correct ? | 235 Yes | 51 No |
Answer / saurabh
at the time of starting slip S= 1, so the rotor resistance
which depends on slip i.e.
R2(1-S)/S will be equzl to "0",
i.e. rotor will act as short circuit.
hence initailly motor will draw heavy amount of current.
So in order to reduce this inrush current(5 to 7 times of
rated current), we apply less input voltage at the time of
starting so that input curent will be low(as in case of
star connection) & after some time or specified time input
will be fed in Delta connection.
if u understand this then ok other wise read more books in
details...
Is This Answer Correct ? | 164 Yes | 24 No |
Answer / g.v.suresh kumar
AT THE STARTING OF THREE PHASE INDUCTION MOTOR THE STARTING
CURRENT IS HIGH IT IS DUE TO AT THE STARTING THE BACKEMF IS
0.SO BY USING STARTER WE CAN LIMIT THE STARTING CURRENT
Is This Answer Correct ? | 146 Yes | 57 No |
Starter is used to reduce starting current.starting current
is usually large because of inertia,charecteristics of
motor winding(at starting slip=1,rotor resistance low
implies less back emf).So at starting we use starter .for
example.STAR DELTA starter.by using a starter at least the
switching is improved which is much important for safe and
longer life time use.simply a DOL can be used for lower
rated motors (up to 07 HP)in this case.for higher rated
motors (up to 15 HP)we can use a star delta connection.a
delta connected motor takes 1.7 times line current than a
star connectd motor.think ! at starting the current is
almost halved .Now a days we use drives (power electronics
products which not only takes care of starting of a motor
(improving power factor) also controls it as perrequirement.
Is This Answer Correct ? | 56 Yes | 8 No |
Answer / patanjali
1--it limit the starting current.
2--increase the starting torque.
Is This Answer Correct ? | 75 Yes | 32 No |
Answer / bhavik parekh
starter is reqired for the purpose of reduce starting
current. starting current reduce in starting period so that
starting torque is increase. another thing is that if
starter is not provided than high amont of current flow in
starting beacuase of that it may be chances to damege
itself and alose its adjoining m/c.
Is This Answer Correct ? | 41 Yes | 18 No |
Answer / balasivakami
starter is required to limit the high starting current
Is This Answer Correct ? | 32 Yes | 10 No |
Answer / monika khatri
when the induction motor starts.slip i.e "s" has a value
1...and hence the internal resistance value becomes
0..since resistance is directly proportinal to (s-1)....as
the resistance becomes 0..according to ohms law current
becomes very high.....tha value of current is about 5 to 6
times the full load curent......therefore the motor must
accelerate to high speed ,,which is not possible at "load"
condition.....and hence the motor may burst due to
overheating.............to prevent the motor from bursting
by reducing the value of current we use a STARTER....
Is This Answer Correct ? | 24 Yes | 9 No |
Refernce currents are to be generated using refernce cueernts how can this be done
What are the different sign conventions used in electric circuits?
Please give me the formula stating relation between AC & Dc.
what are the importance of earthing?list different types of earthing.
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
why induction motor's p.f 0.8
what is ground fault in ACB?
What's voltage?
1 Answers Pakistan Atomic Energy Commission PAEC,
When neutral is grounded in electrical circuit?
what is the working principle of dc motor & its application ?
What are all present producing cost of Per KWH of various Fuel?
how to check ac servo motor