howmuch current can carry the 2.5Sqmm copper cable?
Answers were Sorted based on User's Feedback
Answer / vijay khilnani
Dear Sripellirajukumar
I had answered 7 Amps and mentioned the thumb rule for
copper is 2000 Amps per sqaure Inch ( not 2000 Amps per sq
mm ) > You need to read the answer carefully before
commenting . For Your info 1 sq inch = 25.4 x 25.4 = 645 sq
mm. Also copper purity / type of insulation / temperature
rise allowed / voltage drop tolerarable would be other
factors which need to be considered. For this 2000 Amps / Sq
inch has a generous margin ie it is has some safety margin .
Vijay Khilnani
| Is This Answer Correct ? | 71 Yes | 17 No |
Answer / jokemaster
its the cable to carry the current and not the current to
carry the cable.:-)
| Is This Answer Correct ? | 38 Yes | 16 No |
Answer / ayad basha
The general thump rule is one square inch copper conductor
will carry 1000 Amps and that of for aluminium conductor is
600 Amps. So, for Cu, 1sqmm = 1.6 Amps appx. and for Al 1
sqmm = 0.9 Amps.
but this will not fit for the increasing cable sizez.
for example for 400Sqmm cable, it will not carry 400 x 1.6=
640 Amps. That is the effective current density of the
conductor decreases as the conductor size increase.
Also depth of cable laying, ambient temperature and cable
grouping also should be considered.
| Is This Answer Correct ? | 29 Yes | 17 No |
Answer / sripellirajukumar
ya mr vijay khilani ur answer might be correct but first u
have to mention the thumbrule ..instead of that u said rule
in ur first question..ok ur answer might be correct...
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / him
Around 15 Amp if cooling is natural . Thumbrule 6 Amp per
Sqmm
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / s.m murshed monowar
2.5 sqmm cu cable which voltage drop /mm is 9.7 ,it will
carry 16 amps maximum distance 30 meter & it will carry 20
amps for maximum distance 25 meter
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / npatra
It depends for which you are using.
1. Inside wall it's maximum capacity defined is 16Amp.
2. For Equipment its's Maximum Capacity defined to be 25Amp
| Is This Answer Correct ? | 4 Yes | 3 No |
What is disadvanage if power factor goes to in leading..?
induction 3 phase motor terminal connection
PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)
if u have single phase load (un balance) and the main power cable is 3.5core means netural is .5 of phase and can the three phase current make the return paht in .5 neutral.
Please define ohm’s law for a.c (alternating current)?
Why does the radius of armature is less than the radius of pole shoe?
can we do the star delta connection of capacitor for 3- phase motor starter.
when we put inducter in neuteral grounding of genrator.
what is diff btw electric,magnetic & eletromagnetic field
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.
what is the capital of india
13 Answers eInfochips, Reliance,
for selection of transformer we will considering 5 to 6 times of starting current of higher rating motor connected to secondary side. according to process wise we will start the motors gradually suppose if we will start 15 to 20 motors at a time wat will happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)