what type of oil is used in transformers? a)conduting b)
insulating
Answers were Sorted based on User's Feedback
Answer / pundlik m wanwe
the oil used in the transformer is mineral oil having the
insulating as well as cooling properties.
there are two types of mineral oil used in transformer 1)
parafinic based 2) napthanic based
| Is This Answer Correct ? | 112 Yes | 5 No |
Answer / richa
the oil used in transformer having the properties of
insulating as well as cooling
| Is This Answer Correct ? | 63 Yes | 5 No |
Answer / raman jain
The oil used in Transformer is to provide Insulation and
cooling.
BDV value of oil should be more than 80 kV for Power
Transformers.
| Is This Answer Correct ? | 57 Yes | 22 No |
Answer / zahir banaso
##the oil used in the transformer is mineral oil having the
insulating as well as cooling properties.
##there are two types of mineral oil used in transformer
1) parafinic .
2) napthanic .
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / gunnam santosh
mainly used to insulate as well as cooling
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / nitin sharma
the oil used in transformer is insulating and it provides
cooling also it is used to insulate two windings from each
other
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / siba prasad
1.now a days synthetic insulating fluids known as ASKARELS(trade name)are used.
2.one such fluid known as PYROCLOR is extensively used due to its remarkable stability as a dielectric strength & have no detorioration through sledging,oxidation,acid & moisture formation.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / mahesh s
insulating oil is usually a highly-refined mineral oil that
is stable at high temperatures and has excellent electrical
insulating properties. It is used in oil-filled transformers.
That is mineral oil
| Is This Answer Correct ? | 5 Yes | 1 No |
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
how can we measure rotor current of a 3phase wound rotor induction motor connected to liquid resistance starter
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
What is meant by stator? What is meant by rotor?
how cables go in and come out for distribution from the feeder pillar box?
what type of earthing is done on hilly rocks.
Explain what is use of lockout relay in ht voltage?
how to calculate the bus-bar size. give formula with description
what is use of mccb.
How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?
what is the difference between power transformer & distribution transformer and what are their ratings respectively?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)