Answer / k.prakashchandra

The current is about 120 A. But it is not continuous.You
have to the study the list of OH conductors available in the
market.For 120 A and 50' Temp rise ,weasel ' ACSR conductor
is enough. Then you have to consider voltage regulation
which should not exceed 6% and further development. Rabbit
ACSR conductor is the next one with carrying capacity of 148
A for 30' temp rise and 183 A for 50 ' temp rise.Temp rise
is for calculation of maximum sag.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the application of dynamic Breaking resistor in inverter ? & How it works ?

2 Answers  


what is earthing transformer? draw the winding dia.of earthing transformer.

0 Answers  


take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????

0 Answers  


EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?

0 Answers  


How can we measure the frequency of a rotor running in full load condition? Explain the method of measuring.

2 Answers   Wipro,






what are iron and copper losses

4 Answers  


What is meant by full pitched winding?

0 Answers  


Do you know how to measure the earth resistance? if so explain it

42 Answers   ABB, BEL, BridgeStone, College School Exams Tests, Dalkia, Dalmia Group, DEC, Electrical, Genpact, HEC, IOCL, JLL, L&T, MSEB, Saraca, Sical, Telecommunications, University Exams,


What is the Difference Between the SCADA & PLC ? Both it also control and Supervise Then what Special in Scada & PLC?

1 Answers  


how can I improve the current at same voltage? if yes is there any circuits?

2 Answers  


Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,

4 Answers   L&T,


why and how current drawn by battery charger depends upon the altitude where it is located?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)