how calculation to be done of cable size/o.h. conductor
size of 11kv h.t.for the load of 2175 kw
Answer / k.prakashchandra
The current is about 120 A. But it is not continuous.You
have to the study the list of OH conductors available in the
market.For 120 A and 50' Temp rise ,weasel ' ACSR conductor
is enough. Then you have to consider voltage regulation
which should not exceed 6% and further development. Rabbit
ACSR conductor is the next one with carrying capacity of 148
A for 30' temp rise and 183 A for 50 ' temp rise.Temp rise
is for calculation of maximum sag.
Is This Answer Correct ? | 1 Yes | 0 No |
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
what is earthing transformer? draw the winding dia.of earthing transformer.
take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????
EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?
How can we measure the frequency of a rotor running in full load condition? Explain the method of measuring.
what are iron and copper losses
What is meant by full pitched winding?
Do you know how to measure the earth resistance? if so explain it
42 Answers ABB, BEL, BridgeStone, College School Exams Tests, Dalkia, Dalmia Group, DEC, Electrical, Genpact, HEC, IOCL, JLL, L&T, MSEB, Saraca, Sical, Telecommunications, University Exams,
What is the Difference Between the SCADA & PLC ? Both it also control and Supervise Then what Special in Scada & PLC?
how can I improve the current at same voltage? if yes is there any circuits?
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
why and how current drawn by battery charger depends upon the altitude where it is located?